First things first: I wouldn’t bother with Victron ESS in the United States, too complicated and unapproved.I'm trying to add the ESS Assistant in the Victron configuration tool. It requires a Grid-Code which is not available for North America.
I like @Adam De Lay approach better, it is more direct.
But since you asked:
You need to signup with professional.victronenergy.com, watch a video, and get the password. Or google cleverly.
For North America, choose Other grid code (not None).
Your ESS will not pass inspections anywhere in the USA, as far as I know (others, please give an opinion).
I’ve been running ESS experimentally from the beginning, and I like the feature set it provides as well.
I select LOM B compliant. I‘ve never seen any power backfed when the inverter is engaged (e.g. during a power outage, or the dozens of times i’ve tested my main panel breaker). So it clearly detects loss of mains properly.
No matter what you do, there will always be the potential for short bursts of power back to the grid, usually when inductive loads are turned off.
The inverters just can’t react fast enough.
One way I minimize this is by using an EM530 grid meter which runs at 10Hz (faster updating), and CTs in my Main panel.
The point of these is to carefully measure how much power goes in and out over the two legs.
Note that measuring L1 at -500W and L2 at 600W is ok, because net 100W is coming in.
I’ve got the old spinning wheel meter, when I push back to the grid, its starts to go backward and then ratchets to a stop.
That’s an old meter. A newer one will detect the power going back to the grid, and probably notify the POCO.
This conversation is of course a whole set of threads on this site, definitely read through them.