Review Pacific Sun Systems / SpecializedPower 24V 200Ah LiFePO4

krby

Solar Enthusiast
Joined
Nov 2, 2019
Messages
266
Location
SF Bay Area, CA
Note: I am not affiliated with the company, and have not been compensated in any way for this review, I'm just a customer and I don't see much info about these batteries on this forum, so I thought I would share my experience.

In a few different posts people have asked about the LFE packs available from PacificSun Systems or SpecializedPower.net. I bought a 24V 200Ah LFE pack from them. It arrived a few days ago and I just got done doing a couple of charge/discharge cycles.

TL;DR / Summary
The battery took longer than I expected to arrive, but that was a misunderstanding on my part. So far in two charge/discharge cycles, I've gotten a little over 4.4kWh of usable AC power from my inverter, so the pack appears to be as advertised. I'm a happy customer! Also, I haven't taken the battery apart, so now teardown report here.

Ordering thru Delivery (Nov 11th - Dec 26th)
I started off looking at the Pacific Sun Systems website, as soon as I started looking at the batteries, I was redirected to Specialized Power Systems. Both websites say that Specialized Power is battery division of Pacific Sun. I looked around a bit over about a week, and finally decided to order. When I placed the order, I had trouble getting the website to accept a credit card. I ended up selecting "Cashier's Check" as the payment option, submitting the order, then emailing the company. Within a few hours, they had me sorted out. As promised, the next morning I got an invoice to pay via PayPal (I used a credit card via PayPal). Given the lack of reviews or experience with this company, I was nervous about the whole thing, but hopeful.

It appears each battery is made to order (in China, I assume) so you can customize a few things like M10 terminals or Anderson SB connectors, BMS current limits, etc. When I ordered, I didn't realize each battery was built on order, or may have asked what other options there were for shapes and and cases. If anyone is considering ordering, I encourage you to reach out to them via email, they were very very helpful.

Because this is made to order, the lead time was longer than I expected. I missed the part of the website where they say 15-20 business days before shipping. This was my mistake, and I probably frustrated the sales/support guy Zack by being so impatient. In my case, payment was made on Nov 12th and I got a FedEx tracking number on Dec 17th. Shipping was by a freight forwarder then to FedEx. Looking at the tracking history, FedEx got it on Dec 23rd and I had it at my door on Dec 26th. I'm giving all this detail so that if other people order, they don't worry like I did and know that this delay is a normal experience.

Battery / Setup
The battery arrived in a pretty abused FedEx cardboard box. FedEx left it on my porch upside down (there were clearly "up this way!" arrows all over the box). Inside the cardboard box was a wood crate with a hinged lid and latch. Inside the wood crate, the battery was really well padded with foam. The battery on its own weighs about 90lbs and is in a metal case with M10 terminals on it. It has an LCD Volt Meter mounted in the case. I'm 99% it is this one from DROK, I have asked them to confirm (have I mentioned how helpful they are via email?) Also included was a Chinese/English manual and a pair of 2/0 cables (maybe 2-3ft) with crimped M10 lugs. This was good, because I had planned on M8 lugs and had only 5/16th gear ready!
batt.jpg
The manual looks like it's maybe from whoever manufactured the cells. It suggests:
  • Bulk / Absorb voltage: 3.65V x cells (3.65V x 8 = 29.2V). This feels high, and I had trouble charging at this setting, so for the tests I used 3.5 x 8 = 28V)
  • Absorb cut-off voltage: 0.01C (200Ah x 0.01 = 2A) <-- My Victron MultiPlus won't do current-based ending of the Absorb stage, so just made the Absorb time as short as possible, 1hr.
  • Suggested charge current: 0.2C (200Ah x 0.2 = 40A). I’m charging at 50A (0.25C), and asked them to set the BMS to allow at least 50A charge current when I ordered.
  • Discharge cut-off: 2.5V x cells = (2.5 x 8 = 20V) This seems too low, so I set my Victron at using 2.875V x 8S = 23.0V
I initially had trouble charging at 3.65V, as the battery got close to 29V the Victron warned about "Battery Voltage Ripple", and the charger kept stopping, pausing and restarting. I suspect the BMS was cutting out and turning back on. So, after some research I have decided on 3.5V per cell for Bulk/Absorb, and setting float voltage to 3V, based on some advice from the Victron forums, the idea being the float stage doesn't do anything. I have sent questions to the folks at Specialized Power to confirm the charge and discharge voltage limits, I hope to have answers in a few days, but the holidays may delay that.

For my build, I'm using a Victron MultiPlus 24/3000 Inverter/Charger. I don't have the final case it all goes in, so I hacked up a 14AWG extension cord for AC in and out to the MultiPlus. Don't do this for anything but bench testing. The battery has a terminal mount 200A mount fuse on it, but with this temp extension cord, I've left out the fuses on AC in and AC out. Those will go in my actual build.
wired and ready for test.jpg
I really wanted to do a larger load and more controlled test. My original plan was to use this to use my EV charger as a load, but the night before I realized that I this Victron unit outputs 120V, my EV charger is 240V, and even if I could make it operate on 120V it would only use about 12A. In the US, they're usually designed for 80% of a typical 15A outlet. So, to get the tests running quickly was limited to 120V household appliances. The Victron MultiPlus has two separate AC Out terminals. I could have wired up another line, but I only had one extension cord that was in the junk bin. In the end, I used a space heater, that is rated for 1500W. It's cold in the garage, so it wasn't completely wasted energy!

Test1
After an aborted charge (see my notes above about the BMS maybe cutting out). I measured the batt at 26.65V with a trusted DMM. The LCD said 26.6V, the Victron said 26.64V. I plugged a Kill-A-Watt and my space heater...
testing with space heater 1.jpg
Other folks on this forum have noted that a Kill-A-Watt may melt with extended loads of high current. To help with this, I ran a fan (from house AC, not the inverter) across the Kill-A-Watt so that it blew on both the front and back plugs. For my 3hr tests, this worked fine.

During the test, my AC load was about 1450W. To lower current a bit, I eventually changed the output AC on the Victron to 124V. My research suggests up to 126.5VAC should be ok. The Victron app had these numbers during one snapshot I grabbed: DC In - 25.87V 61.30A. AC Out - 1441W (I didn't record the volts and amps).

At just under 3hrs, the low battery light tripped on the Victron. I stopped the test manually at 3h1m:
  • Kill-A-Watt had 4.34kWh of AC used.
  • Battery LCD shows 24.3V under almost no load (25W) right after I stopped. 10m after stop: 24.8V, 28min after stop: 25.0V
A while later I started charging with 28V as the bulk/absorb voltage. Charge current is limited by AC-in of about 1450W. About 5hrs later I was going to bed and didn't want it running overnight. Charger was in absorb phase holding at 28V. I turned it all off.

Test2
The next morning, the battery had dropped down to 27.2V, I believe this is considered nearly full? The one wiring change I made was to add a 16AWG v-sense wire from the Victron to the battery. My goal was to make sure the Victron had a more accurate reading of the battery voltage, but in practice I'm not sure how much the helped. 40-50A of current at 25-26VDC over 5-6ft of 2/0 cable doesn't have much drop. I turned on the charger a bit, and it was immediately in absorb phase.

09:34a - Start. Battery was at 27.5V under no load
09:34a - Victron software showed DC In: 26.31V 61A. AC Out: 124V 11.91A, 1460W
11:35a - Victron low battery light turned on. I had this set to 25.5V, I changed it to 25V
11:36a - Victron software shows DC In at about 25.53V 63A (changing rapidly)
12:40p - I came back to find the heater turned off! Low voltage cut-off may have tripped?
12:41p - Kill-A-Watt said 4.42kWh used.
12:50p - Battery at rest shows 24.7V. Restarted the load.
12:53p - Under load Victron software shows 24V 67A and voltage dropping quickly, so I stopped the test.
12:54p - No load, battery voltage recovers back to 24.00V
01:05p - Battery at 24.21V
01:24p - Battery at 24.30V (DMM shows 24.28V)
Final Kill-A-Watt total is 4.47kWh.

A few times I calculated between 87-90% efficiency in the inverter (DC In vs AC out), this also includes the power to run the Victron itself. So I think 4.47kWh of AC out is about 5kWh of DC from the battery, which is more than I should be pulling from it, but I think this tells me that I did get the battery I expected!

Looking forward to your comments and questions.
 
A quick update, the guy from Specialized Power, Zach, says he may start carrying some packs in stock:
I hope to have 12V200AH, 12V400AH and 24V200AH in stock starting next month.

I don't know if he's the owner or just works for the company, but he was and continues to be great to deal with.
 
So apparently (I've got an email) I am allowed to open the outer metal battery case without voiding the warranty, as long as I don't mess with the components. If I get up the nerve, I might do this to just take pics.
 
Last edited:
@krby IF you have an email that he states you can open the box to inspect it & the components used therein DO IT ! Photograph every step of it. There will be a cover over the battery cells which should be easy enough to pop off to see what cells are there (look for the markings and QR codes) and to see what they wired & how. I have read good comments about Pacific Sun and do not recall seeing any negatives but I haven't seen anything recently. Just take your time, don't rush and don't force anything, the screws will likely have some Loctite so do take that into account. Importantly ! Make sure you use the proper sized Phillips screw driver (nice & tight in screw head) otherwise you will strip the head (the screws are softer steel, similar to those used on computer parts).
 
There are a bunch of companies that offer these LFP units from USA warehouses already. Maybe not identical but same chemistry and similar performance characteristics. I put a 30kWh bank from Ohmmu Energy on my house and love them.
 
I did get an email stating I could open the battery without voiding the warranty. The cable lengths made it difficult to move the lid around without pulling wires so this was really quick look, but didn't disconnect anything or move much around. It looks like the cells and BMS are held in place by hard foam, some glue / sealant, and what looks like some reinforced packing tape.

Hopefully this is useful to someone.
 

Attachments

  • 01-outside.jpg
    01-outside.jpg
    73.8 KB · Views: 97
  • 02-overview.jpg
    02-overview.jpg
    196.2 KB · Views: 101
  • 03-overview.jpg
    03-overview.jpg
    179.2 KB · Views: 102
  • 04-BMS-terminals-voltmeter.jpg
    04-BMS-terminals-voltmeter.jpg
    103.8 KB · Views: 96
  • 05-BMS.jpg
    05-BMS.jpg
    151.9 KB · Views: 95
  • 06-BMS again.jpg
    06-BMS again.jpg
    173.1 KB · Views: 95
  • 07-inside lid.jpg
    07-inside lid.jpg
    74.2 KB · Views: 93
  • 08-voltmeter.jpg
    08-voltmeter.jpg
    54.7 KB · Views: 83
I just received 3 of the 24V 200 AH Specialized Power batteries for our off-grid cabin system and will be hooking them up next week. My only complaint so far was lead/shipping time. I ordered early December of '19 and received them last week, right at 3 months! They were built and configured in China then by boat to California and finally by Forward Air to me.

OBTW, the meter in mine is not a DROK unit, at least it's not like the one I have. The one integrated into the battery assembly reads just volts and a bar-braph for SOC.

Not to hijack but here are a couple pics of my batteries. Note that the battery case I specified is different.
 

Attachments

  • Crate.jpg
    Crate.jpg
    82.6 KB · Views: 33
  • Crate opened.jpg
    Crate opened.jpg
    61.7 KB · Views: 37
  • Battery top.jpg
    Battery top.jpg
    49.7 KB · Views: 37
  • Charge indicator.jpg
    Charge indicator.jpg
    46.2 KB · Views: 39
  • 3 batteries.jpg
    3 batteries.jpg
    60 KB · Views: 37
Last edited:
I installed my three batteries middle of last week and it's been pretty much solid rain since! Nice to be able to go a few days without sun.
 
According to their web site the current price is $2750/ea shipped. I got mine a bit cheaper due to a "black Friday" sale but I can't remember exactly how much.
 
Not to hijack but here are a couple pics of my batteries. Note that the battery case I specified is different.
Aren't those Pacific Sun ? I like the case setup, that looks good, I am curious how the cells are setup inside though, I can picture a couple of ways to do it. I don't suppose you're going to open them up, :LOL:. Give the folks a link for those too, so they can check'em out.
 
I am curious how the cells are setup inside though, I can picture a couple of ways to do it. I don't suppose you're going to open them up, :LOL:. Give the folks a link for those too, so they can check'em out.

I guess those are just a shape than mine, but same capacity.
 
These are the batteries I have:

https://pacificsunsystems.com/catalog/product/24v-200ah-lifepo4/

I have not had the lid off these (kinda lazy) but I would imagine the construction details are similar to the OPs battery but laid out a bit differently inside.

They do take the juice, though! When I hooked these up and threw the switch last week they pulled almost 80 amps (77-78) for most of the day when the sun was not behind a cloud. Never saw my Classic 200 put that much out before, maybe 40 amps...

Mine are pretty much a spaghetti-farm right now until I get my heated/insulated enclosure built. They are sitting on milk crates with cables running up to my bus-bars. Sorry about the huge size but I'm at cabin with laptop and no PhotoShop on it...

DSCN0029.JPGDSCN0031.JPGDSCN0034.JPG
 
Last edited:
I've maxed out the Classic-200 which is limited to 79A for 24V. Spring project is more panels and another classic with follow me, as 910AH LFP bank goes online quite soon. I can hear the Classic's fans howling inside the powerhouse when I am standing outside with the door closed LOL. Going to have to do that 5 year "refresh" deal I guess pretty soon.


Yes, your case is tall & narrow from the pics, so I winder how they stacked & wired the cells in there. The Pics Kirby posted a really well built setup, pretty impressive to my eye. I was just looking at their site, they have the same but Cold Weather with heating element for $3500 while the regular one is $2750, geez louise….
 
When I bought mine they didn't have the cold weather version but they do seem awfully pricey. I am going to build an insulated cabinet to keep them in with the batteries sitting on an aluminum plate with a 7.5 W RV "elbow heater" stuck to the bottom of the plate.

If I get bored maybe I'll remove the lid and take some pics...
 
I like that the white ones also have a circuit breaker. Both may be sold by "Pacific Sun" but I dont think those are from the same manufacturer. Pacific Sun just seems a reseller of alibaba dealers.
 
I like that the white ones also have a circuit breaker. Both may be sold by "Pacific Sun" but I dont think those are from the same manufacturer. Pacific Sun just seems a reseller of alibaba dealers.
While I was talking to them, it felt like Pacific Sun either spun off Specialized Power to handle just batteries or they partner with them. Who knows, maybe the same people just different business entities. Regardless, if you buy from the Pacific Sun website, you'll get redirected to the Specialized website and end up buying from Specialized Power.

From what I could figure out talking to them, a small number of batteries are "in stock" but nearly all of them are made to order. I don't know where they get their cells or where the assembly is done.
 