AntonieCebu
New Member
- Joined
- May 21, 2022
- Messages
- 18
Hi,
We have a new PowMr 5KW Hybrid inverter setup with 8x450W Panels and a 10KW / 200ah Battery.
Now the system doesn't switch over to solar (Stays on bypass) and in order for it to use solar and my installer says we are lacking panels and need to add 2 panels more as the Nominal Operating Voltage for the inverter is 360VDC. When measuring using a multimeter we are at 350VDC. I'm assuming my installer is correct but I wanted to check with you guys as well.
Also if so does this mean that 360VDC is the minimum and what would be the maximum? We are planning to by a secondary Hybrid Inverter and additional battery to run the system in Parallel for a 10KW setup (Eventually adding in more panels)
Any thoughts and ideas are welcome.
Thank you!
We have a new PowMr 5KW Hybrid inverter setup with 8x450W Panels and a 10KW / 200ah Battery.
Now the system doesn't switch over to solar (Stays on bypass) and in order for it to use solar and my installer says we are lacking panels and need to add 2 panels more as the Nominal Operating Voltage for the inverter is 360VDC. When measuring using a multimeter we are at 350VDC. I'm assuming my installer is correct but I wanted to check with you guys as well.
Also if so does this mean that 360VDC is the minimum and what would be the maximum? We are planning to by a secondary Hybrid Inverter and additional battery to run the system in Parallel for a 10KW setup (Eventually adding in more panels)
Any thoughts and ideas are welcome.
Thank you!