Recent content by BackTOschool

  1. B

    Combiner box limits?

    Thank you, for your time in answering my questions. kind regards Steve
  2. B

    Combiner box limits?

    Hello, I would be really grateful for experienced persons thoughts / input as I'm trying to avoid a mistake.... I have a 2S4P system that I am installing. 8 identical Panels, each panel: 330W, 32.6V (VMP), 10.2A (IMP) 10.9 (ISC) My array is East / West, as a result I am over-panelling. My...
  3. B

    Is it looking ok ?

    Thank you, you have been an enormous help, steve.
  4. B

    Is it looking ok ?

    Thank you LakeHouse, your explanation is helpful. Steve
  5. B

    Is it looking ok ?

    Thanks for your answer, If I've understood what you have said, in summary: 1: Although the array can generate a theoretical 2,640w, the MPPT will throttle that to a max of 1015w, which is within the 1080W limit of the combiner box ( so it's what is flowing through the combiner box, not what...
  6. B

    Is it looking ok ?

    If I could ask..... In the parameter data for the 6 string Eco-Worthy combiner box that I intend to use, it states the following: "Max input solar system wattage (12v) = 1080W" "Max input solar system wattage (24v) = 2160W" "Max input solar system wattage (48v) = 4320W" My battery is a single...
  7. B

    Is it looking ok ?

    Thanks very much, I will proceed........ kind regards Steve.
  8. B

    Is it looking ok ?

    Hello Sunshine_eggo, could I just check something else with you please? This is my thinking for cabling purposes: With my 2 string 4 parallel array, each string will create 2 x 38.12v ( 76 v ) and 1 x 10.2a. I am intending to use the: ECO-WORTHY 6 String PV Combiner Box & 63A Circuit Breakers (...
  9. B

    it's all in the connections

    I'm nearly there... advice please: My system: 2S4P, each string has 2 x 330w panels, each panel output is: 32.6v (VMP), 10.2 (IMP), & 10.9 (ISC). this gives a max output of 2640w to the charge controller. QUESTION: 1: Do I HAVE to use a combiner box, or could I use the standard mc4 connectors...
  10. B

    Is it looking ok ?

    Thank you very much. steve.
  11. B

    Is it looking ok ?

    I do not have a data sheet, the numbers are direct from the label on each panel, thanks you have been very helpful. Can I please one final question: (just ask for my own education): The fact that the power is coming from 2 panels, (not 1) on each positive cable, does not require a larger...
  12. B

    Is it looking ok ?

    Hello Sunshine_eggo, Thank you for taking the time to read and comment, it is appreciated, your comments are well received. I have a E/W array, half on east side, other on west side. This is why I am over panelling, thanks for your observations. Concerning fuse size, here is the data on the...
  13. B

    Is it looking ok ?

    Hello, I am about to mount a further 2 panels to my small emergency system, and I would very much appreciate if an experienced person here ( not a newbie like me- thanks) would take a quick look and comment if it's wrong! ( or right ? :) ) Please take a look at my numbers / panel configuration...
  14. B

    WHY THE HEAT ?

    who? whole cable
  15. B

    WHY THE HEAT ?

    i have observed the heat starts at the fuse lugs, and then spreads along the cables, until the who cable heats. the last place to heat seems to be the bat terminal. I'll try bypassing the fuse and bolting the lugs together... thanks for you continued thoughts.