Update on 6000XP issue.
Everything is fine unless I combine two strings together in parallel. Either single 5x string is fine for each PV input.
Seeing 2300-2500w per string, if my math is correct 2423w / 190.7v = 12.7a per string.
If two strings in parallel 12.7a x2 = 25.4a hence the PV...
For what it's worth I am in the Midwest (OH) with a 9KW Bifacial Array.
Anything more than 3800w per PV input (200-230v) the 6000xp will switch to grid bypass and I receive "Fault E024: PV short".
After a few minutes the 6000xp will recover, switch back to Solar/Batt, then fault again a...
Sure,
Didn't mean to hijack the thread. Issue only happens during full sun, cloudy days I can run all panels.
2x 5S2P - 450w
Each 5x Series is fused then parallel in combiner boxes. I am able to switch off either string and charge without issue.
Maybe it is due to SOC of batteries?
I have a...