  1. FilterGuy

    Top Balance question

    Patience Grasshopper. Patience.
  2. FilterGuy

    Top Balance question

    As long as the Power Supply is correctly set to the target voltage, there should be no reason to worry about over-charging the cells. At around 3.45 volts the current will start tapering off and the voltage will start going up. This will accelerate till the charge is complete. You have...
  3. FilterGuy

    Top Balance question

    That cell started with a higher SOC or was a 'weaker' cell. This is normal.
  4. FilterGuy

    Top Balance question

    OK. Now it is a matter of being very patient. Set the target voltage on the Power supply before you hook it to the parallel cells and then hook it up and wait. No matter how tempted you are, DO NOT raise the voltage on the power supply.....
  5. FilterGuy

    Top Balance question

    Lets do some math. I assume these are new cells. New cells generally come at ~40% SOC. 16 280Ah Cells in parallel will need .6 X 16 X 280 = 2688 Ah to fully charge. At 20A this will take 2688/20=134Hrs to fully charge. Yes, it is normal. Keep in mind that at 3.3V 20 A is only 66W...
  6. FilterGuy

    Creation of vertical development lifepo4 bench

    I don't have a reference, but have thought about it some. The idea of a very flat profile pack is intriguing to me. If you decide you need cell compression, these layouts could be challenging.
  7. FilterGuy

    ACK 175 fuse for 3000 W POWMR 24 v inverter / charger

    The spec sheet says 10KA interrupt. That is lower than the class C but better than most other types of fuses.
  8. FilterGuy

    DIY Inrush Current Limiter solution needed

    No. The best resolution is to make sure the cells are balanced and the BMS never shuts off.
  9. FilterGuy

    Engineering mindset video on breakers and why they don’t protect life

    Nice video. It is true that a breaker will not protect you from direct contact with the hot wire . However, what is not mentioned in the video is that a breaker in conjunction with a neutral-Ground bond will save lives if the short is a ground fault.
  10. FilterGuy

    is this guys wire size calculator off or is he inputting an extra valid variable ?

    I have not run numbers but I suspect his calculator is using the ABYC tables (American Boat and Yacht Council). These tables are much less conservative than the NEC tables. The reason I suspect this is two fold 1) he is an RV builder and a lot of RV builders us the ABYC tables. 2) His...
  11. FilterGuy

    Combiner Box Fuses and Breakers

    That sounds correct. To be code complaint it should be outside.
  12. FilterGuy

    Combiner Box Fuses and Breakers

    They might exist, but I don't know of any Tigo sells two systems. One is just the rapid shutdown system and the other is an optimizer system that will also do the rapid shutdown. (The Cloud Connect is for the optimizer system that has the cloud internet connect) The rapid shutdown system...
  13. FilterGuy

    Combiner Box Fuses and Breakers

    The rapid shutdown requirement has been in the NEC since 2017(?). It is not just CA. I don't know about 'shorting' the panels. I had not heard that before. I guess if the VOC is high enough on the panel it might be needed. Most systems these days use a signal imposed on the power lines...
  14. FilterGuy

    Combiner Box Fuses and Breakers

    The max series fuse question is a good one. If we just add the two Iscs together, two strings are still under the 20A. The NEC requires two 1.25 multipliers (That is where the 1.56 comes from). The first 1.25 multiplier is to cover any extra current due to the Isc only representing...
  15. FilterGuy

    Combiner Box Fuses and Breakers

    With only two strings, you do not need fuses at all, but you do need an 'accessable' disconnect. (In NEC terms, 'accessible' means 1st responders can get to it.) Fuses or breakers are only needed when there are 3 or more strings. However, you do have to size the wires correctly. The NEC...