Very interested in this but I'm seeing a lot about connectors and stuff thats over my head. I'm a newbie building my own 48V system.
This looks like just what I would need, and doesn't cost too much more than me building it myself (and I'm sure this is a lot cleaner).
any advise? I have 16...
Sadly their new "modified" military discount does not apply to most good stuff. Tools, lumber, wiring, major appliances. basically
all the stuff you would want to use it for. However I have a local lowes that uses that more as "guidlines", but the store in the town where I work goes by the book.
Thanks, Lowes actually has it $40 cheaper.
https://www.lowes.com/pd/Southwire-SIMpull-500-ft-6-AWG-Stranded-Black-Copper-THHN-Wire-By-the-Roll/50101714
yes exactly, I was originally going to go 2S3P, this array would require 2 gauge wire.
going to 3S2P will allow me to use 6 gauge wire, but my CC would not handle the nearly 200 amps so I am returning the midnite 150 and
getting the midnite 200.
this saves me over $700. which will buy over...
If I wire my panels the this way
3S2P
then it would be
3S = 3X Voc/Vmp
2P = 2X Isc/Imp
or
132.9 VMP
21.06 ISC
for a length of 230 feet in plastic PVC
I plug this into the calculator and it says I can use 6 gauge wire with a 2.89% voltage drop. this way will save me around$1,000 vs having to...
Charge control is a midnite solar 200, the panels are 440watt panels, according to the calculator my array wired 3S2P will only need 6 gauge wire vs wiring it 2S3P would require 2 gauge to keep loss below 3%
Well after several Discussions and listening to several people On here I have decided to go with a 48v system.
The big bonus with this is I will save over $700 on wire from my panels since I hav s 230 foot run and wiring my panels 3S2P will allow me to use 6 gauge wire vs 2 gauge wire.
I...
Yes, I will be using a midnight 200, I have a 150 but I have already talked to the power store and they are going to let me exchange it
minus a 15% restock fee. after doing the math and counting everything, the restock fee, shipping the new one to me etc I will still save $732.
with will get me...
OK, can you check this for me
thank you, can you double check my math?
if I wire my panels the other way
3S2P
then it would be
3S = 3X Voc/Vmp
2P = 2X Isc/Imp
or
132.9 VMP
21.06 ISC
for a length of 230 feet in plastic PVC
I plug this into the calculator and it says I can use 6 gauge wire...