  1. K

    Solar configuration

    Won't that be danger for the wire? Can I use a 16A 1000V TOMZN breaker between my panels and Inverter as a on/off switch? I have 6S 230w panels. 230x6=1380w Vmp=30v so 1380/(30x6) = 1380/180=7.66A
  2. K

    Solar configuration

    Ok, thanks. Why should breaker be 1.25 X wire rating?
  3. K

    Solar configuration

    Ok thank you. So according to the UL battery cable ratings I can use 2awg cable for 178A? Is this correct? Or should I go up to 1awg rated for 208A? Would it be feasible with a 200A breaker og should it be exact 222,5A with a 2awg wire? How exact should the numbers be?
  4. K

    Solar configuration

    Ok, great. Thank you! Where can I find a reliable wire rating chart? Is this reliable? So wire size for 182,2A is 00awg (67,4mm2) wire?
  5. K

    Solar configuration

    I see. So for sizing for the 182.2A DC input listed: Is it correct that 4awg (25mm2) 7feet wire can handle 150-200A? And together with 4awg wire I should use a 180A circuit breaker?
  6. K

    Solar configuration

    Ok. Not size for the 120A DC output listed?
  7. K

    Solar configuration

    Thank you very much! 😊 How to determine wire size and circuit breaker between inverter and battery? My battery is 48V 270ah (13kwh) Here is the inverter:
  8. K

    Solar configuration

    Ok. But according to your "1.25X the wire rating" statement I should have a 25A breaker when using a 13awg wire which is good for 20A? This is for protecting the wire?
  9. K

    Solar configuration

    Ok nice. I've already a 2.5mm (13awg) wire buried from the garage to the battery shed. What about my 63A circuit breaker, is it pointless to use?
  10. K

    Solar configuration

    Ok, I've bought a 63A breaker, it's maybe too big? Wiresize: is this correct?: I have 6S 230w panels. 230x6=1380w Vmp=30v so 1380/(30x6) = 1380/180=7.66A So I have to use a wire that's good for 7.66A? 1.5mm2 (15awg) wire is good for 15A so it should adequate?
  11. K

    Solar configuration

    Where is the "max fuse" value on this? Should it be listed here?
  12. K

    Solar configuration

    Ok, thank you, then I'll go for 6S Ok, no fuse in 6S configuration. Anyway I want a breaker to cut the power if I want to. What size circuit breaker do I need before the inverter? Ok, so strings is the same as parallel.
  13. K

    Solar configuration

    The same with this inverter? I have a Voltronic Max 8kw. Is it possible to have 3s2p? It's often shading on three of the panels... And what size circuit breaker? I assume I don't have to fuse the panels in 3s2p configuration? I don't understand the manual with the recommended solar panel...
  14. K

    Solar configuration

    I have 6 230w panels with following specs: Voc: 36.9V Isc: 8.31A Vmp: 30.2V Imp: 7.62A What is the best panel configuration for the MPP MAX 11KW?
  15. K

    Ferrule on circuit breaker?

    Yes it has clamp style terminal. How tight should it be? Should it be impossible to take it apart with the bare hands? I tightened it the hardest I could but I can take it apart with the bare hands...