This is the DC connection area of the inverter
Should connect +1.1 , 1.2 ,1.3 and negative 1.1 , 1.2 ,1.3
and then measure polarity and voltage of each?
The wires going to the inverter are extensions with MC4 connectors at the roof panel side-not connected right now
That is what I will do in a bit . Connect the 6 wire + ground to the inverter
connect MC4 to the extensions
Verify that the voltage and polarity at the inverter connections are...
Thanks for the answer. Should I consider a hybrid inverter in case I do not make the deadline of 31 December when Net Metering expires in Illinois?
Also I got quotes for 10kw and 15kw or should go with 20kw? It will be installed on flat roof with non-penetrable ballasted bracket system
The wires going to the inverter are extensions with MC4 connectors at the roof panel side-not connected right now
That is what I will do in a bit . Connect the 6 wire + ground to the inverter
connect MC4 to the extensions
Verify that the voltage and polarity at the inverter connections are...
here is the panels inverter setup report
I also open a new thread https://diysolarforum.com/threads/help-with-on-grid-3-phase-fronius-inverter-combiner-box-wiring.95579/
Do you recommend any solar system supplier from China? I am in communication with Sunark and they manufacture the Sunevo solar panels. Are they good? thanks
will this combiner box would work? amazon Hardcover Solar Combiner Box with 4 Strings, 80 A Circuit Breakers. This pv Combiner Box is Suitable for Off-Grid Solar Power High-Power Version
will this combiner box work? amazon Hardcover Solar Combiner Box with 4 Strings, 80 A Circuit Breakers. This pv Combiner Box is Suitable for Off-Grid Solar Power High-Power Version
Should first attach the PV wires to the inverter and then connect to panels?
or Should I connect the PV wires to the panels and then attach to the inverter and then measure polarity ?
13 x 3 panels series
DC voltage 700VDC 10 Amp - 3 strings 6 wires + ground wire
I do not want the wires to...
Hi what diameter conduit should use for 3 strings from panels to inverter? 1 inch or 1 1/2 inch . Also should use metal or PVC conduit and what kind of junction box? thanks
this is from the Fronius inverter manual
"Multi MPP Tracker inverters have two independent DC inputs (MPP Tracker). These inputs can be connected to a number of different modules. Each MPP Tracker has 3 DC+ terminals. There are a total of six DC- terminals. 3
Connecting two–six strings in...
Can anyone suggest a combiner box for 3 strings -39 panels 13 panels per string . Also for the panels extensions that are outside exposed should use different PV wire than the THHN that goes in the conduit. Thanks
I have Fronius Symo 15kw 208V 3 phase . Has a built in DC disconnect
Input Data
Number of MPP trackers 1
Recommended PV Power (kWp) 12,0 - 19,5 kWp
Max. usable input current 50 A
Max. usable input current total (MPPT1 + MPPT2)
50 A
Max. array short circuit current (1.5 * Imax) 75 A...
If connect the PV wires to the inverters while disconnected from panels
After connected to inverter - plug the MC4 to the panels to measure voltage and Amps
built in DC disconnect at inverter Off and AC Off
Hi I have 39 x 415W panels arranged in 3x 13 panels 3 strings . I have a Fronius Symo 3 phase 15 kw inverter. What type of combiner box DC do I need for the 3 strings . Any suggestions . thanks
I have 39 panels and I will have 3 strings (13 panels per string ) is THHN 10 AWG wire good for conduit us? Also is your junction box in the picture closed to the inverter or on the roof? thanks
Hi how many panels should use with Fronius Symo 15kw 3 phase 208V?
Fronius Solar Creator says between 12.33 kWp and 17.5 kWp while the Technical Data says
Recommended PV Power (kWp) 12,0 - 19,5 kWp
Hi I am working to use Fronius 15kw 3 phase 208v with an input PV between 12kw and 17.5kw. Yah I was offered your setup with 3 single phase inverters to run 3 phase inverters. But since I have 3 phase from the grid and this will be grid tied the power company recommended to use 3 phase...
I need some help finding and installing rapid shutdown to the solar panels. I am looking at FireRaptor , Tigo and APsmart
Anyone has experience installing and using any of these?
Any help is welcome. Thanks
I am planning to order a DIY kit 20kw 3 phase 36 panels 575W with 20kw 3 phase Growat inverter from China. I applied to the power company for Net Metering and interconnection Did not apply yet for city permit in Illinois. This is a self-install -will hire an electrician for interconnection
I...
Hi here id the Fronius Symo creator report. I need some feedback on wire size -if 10 AWG will work
Also the report says needs
String fuses required
String combiner/Y-connector required What type of combiner box should use?
Has anyone had experience with or installed a solar stack mounting system? I am considering the use of solar stack system on an asphalt flat roof to avoid the additional weight that comes with ballasted mounting systems. Thanks
Did they install one at each panel? What inverter do you have-is it connected to the inverter? Can the Ap smart be installed independently with stop button
I understand what Tigo and APsmart use the same technology
I have a Fronius Symo 15kw 208V 3 phase the only model that does not have...
I understand what Tigo and APsmart use the same technology
I have a Fronius Symo 15kw 208V 3 phase the only model that does not have SunSpec PLC or Rapid Shutdown communication
I am planning on installing myself
My inverter is Fronius Symo 15 kw 208 V 3 phase model did not have the RDS option. Any way I can add to the 39 panels an RDS system later on?
Right now all the panels are connected in series in 3 rows of 13 panels
The wires going to the inverter are extensions with MC4 connectors at the roof...
I also have a red home depot 10 AWG wire -will tis work or I should return it
https://www.homedepot.com/p/Cerrowire-500-ft-10-Gauge-Red-Stranded-Copper-THHN-Wire-112-3873J/202304724