Sorry for late response (was sick thanks to this crazy weather)...
I did and was (momentarily) getting the 120v in, but watched it started dropping like it does previously. I'm going to order a heavy duty (10-guage) 10ft. extension cord and replace the input cord I have installed. The cord is...
That's what I'm try to figure out...when plugged in it starts at 120v, then it will bypass battery and drops to 89v in a matter of seconds causing the #10 warning to flash.
I've plugged into several outlets only to get the same issue. I double-checked my AC IN connection to ensure nothing is...
I was able to change the setting #28, thanks.
As for the voltage, I tried plugging in the inverter (with the battery off) and the current remained at 120v without issues for several minutes.
It seems to have problems when I have the battery itself on and AC plugged in...
I also noticed that...
I was able to change that setting, thanks...still working on the other issue.
As for the voltage, I tried plugging in the inverter (with the battery off) and the current remained at 120v without issues for several minutes.
It seems to have problems when I have the battery itself on and AC...
Thanks for both yours and everyone's input...I'm a Noob and getting my feet wet dealing with solar project! My goal is having emergency backup power here in AZ which we have plenty of sun! I already have a 6-circuit Pro Trans switch installed which this setup can power up critical circuits, or...
I have setup an EG4 3000 ehv-48 on a dolly with an Eco-Worthy 48v 100ah battery which is used for emergency backup power. I read posts about the "open-ground" issues and ways to resolve it, however I plan to plug it into a Reliance Pro Tran manual transfer switch when needed for outages.
My...
I only used the EcoFlow once after trying other settings just to see if it made any changes (which it didn't). Everything I've been trying since yesterday has been from home outlet.
Hey Mike,
I have the same setup as Kent...if I understand correctly, since I already have a neutral bond in the main panel which my Pro Trans 6-circuit transfer switch is already connected to that should resolve the "open-ground" or am I missing something and need to add a jumper between the...
Here are the wiring pics, I made sure that all wiring are tight. I don't have my PV connected to anything at the moment because I don't have enough solar power to make it useful yet.
I dropped it down to 50 on the Charging Current (according to Eco-Worthy manual) without success. It is being plugged into a 120v outlet both with and without loads (I have one outlet near my pool which was installed during construction), and has used heavy duty extension cord just to try...
Update:
You guys were right about the cabling gauge…
I thought the cable I installed was 10 gauge, but apparently it was not. I replaced it with an extension cord with 10 gauges and now it charges with no power degradation now!
Now that that problem is resolved, I can focus on the other two...
Tried 30amps using my EcoFlow Delta Max (without any other connections) showing it still pulling over 2130watts...gonna change some other settings and see if that makes a difference.
I recently purchased an EG4 3kw off-grid inverter with an Eco-Worthy server rack battery (51.2v) and just set it up today. It seems to be working fine, but when I plug it into an outlet it keeps flashing Code #10 and shuts down. The inverter is in my shed with lots of circulating air so it's...