Even at 200A it will take some time to trip.
If you can manually operate the switch successfully in both directions at 30A, it is bi-directional and you have done due diligence.
A uni-directional MCCB/MCB will not survive that.
As for establishing the current threshold tolerance, well do you do...
Stick a knife or hacksaw blade alongside it. If there is a magnet inside it, there is no need to test, it isn't bi-directional.
You won't need 160A to test it if it isn't bi-directional. It won't be able to break much less than that ( in the wrong direction) if you just manually switch it.
Just...
BMS capacity aside, and assuming all cells are healthy.
I think you would get away with paralleling an old cell with a new cell at a cell level, as opposed to parallel strings. ( with a single adequately rated BMS).
If you were to run things as parallel strings then a second BMS would be needed...
Sorry gents, I have missed this lively discussion for a while.
The MCBs I tested were from a company called YRO.
I tested them actually to trip for overcurrent conditions, and they don't have any magnetic attractions or repulsions.
Other than that, I have no affiliations and make no guarantees...
I have also considered using a DC generator as a solution.
This is what I may try when I get around to it.
A 96V DC generator through an MPPT. I think that way, the DC voltage can vary, and the MPPT can fine-tune the voltage to the desired charging stage.
I haven't shopped around particularly...
My system has expanded over the years, but if I recall correctly, once I got a Venus device and a BMV shunt, that VRM even reported the total DC from the Outbacks.
I had to enable the "has DC system" setting in VRM or something like that.
As I said, there have been various expansion stages, and...
I ran 4 x Outbacks Mppts without any shunt or Venus device in the system on a Victron Phoenix for at least two years. There was also no comms between the Outbacks. I just used the same settings on each of them and all worked away independently.
You'd do well to notice these symbols on your switchgear:
They are important to identify what equipment is rated for what purpose.
Note: Not all switches are rated to break load current and not all circuit breakers provide adequate isolation.
There will be no current in the circuit to start a fire if the first half does its job.
But like I said prove it by testing, don't take some random guy's opinion over the internet when your house could burn down.
I am in Ireland, but my self-installed scheme is in another country. I don't have any personal knowledge of Irish installers, other than the general knowledge that if you choose to avail of a grant they must be SEAI-approved.