  1. P

    Do we still need T-Class Fuses?

    This makes sense and I think this is what I'll do. Thanks to everyone for the replies.
  2. P

    Do we still need T-Class Fuses?

    So....going back to my main question...am I safe with my current setup of 7 eg4 batteries and an LG6548? no added fuses.
  3. P

    Do we still need T-Class Fuses?

    I have a few EG4 batteries and an LV6548 all in one. The batteries come with a built in circuit breaker/fuse and I'm pretty sure I read the LV6548 has built in fuses. They all connect to the same bus bars. Do i need a T Class fuse for each battery too? Do I not need any more fuses? Am I safe or...
  4. P

    Mixing lithium batteries of different ages

    I added 3 batteries about a year after i got my first 3. There is no noticeable difference that I can see. I'm sure more time will add to that, but I think worst case is that you have some that charge up quicker and you'll lose a little bit of the capacity as those will discharge into the weaker...
  5. P

    EG4 6000EX and power on one of the legs

    All great info guys. Thanks for clearing this up. With all the inverters out, it was pretty hard to see why the 6000ex is not the go to seeing as it does 240v. Nobody mentions this 3000 watt limitation per leg and if you want to wire up your house or a cabin, you have to be careful with 3000...
  6. P

    EG4 6000EX and power on one of the legs

    One thing that I found interesting is that the manual for the 6000ex calls for 10awg wire for the AC output wires. Got me thinking there was no way it supported 6k watts on a 10awg.
  7. P

    EG4 6000EX and power on one of the legs

    The EG4 6000EX runs 240 volts on two legs. Does it max out at 3000 on each leg? If I have a sub panel and one leg goes to one side, the other leg to the other side...what happens if one side of the panel (through a few breakers) wants to draw for example 4000 watts?
  8. P

    EG4 6500 voltage on PV terminals?

    My 6000EX puts out 49-50v DC on those inputs.
  9. P

    40amp or 50amp charge bad for eg4?

    I guess my main concern is that usually it's been my experience that Lithium likes to be slow charged at the higher voltages. I'm worried that doing the opposite could shorten lifespan of my batteries.
  10. P

    40amp or 50amp charge bad for eg4?

    Thanks, but they're separate systems that share the battery bank.
  11. P

    40amp or 50amp charge bad for eg4?

    Each battery has 4ft 2 awg cables going to a 300amp rated bus bar. Inverter 1 has 4ft cables too and inverter 2 has 5ft cables all 2 awg.
  12. P

    40amp or 50amp charge bad for eg4?

    5 minutes max and usually it's like 30 amps and and sometimes hits a minute at 50amps
  13. P

    40amp or 50amp charge bad for eg4?

    My poor memory says I have bulk set to 58v and float at 54v. Batteries are not getting warm as far as I can tell.
  14. P

    40amp or 50amp charge bad for eg4?

    I have 6 of the EG4 48v batteries. They never are all at the same battery percentage according to the BMS software. No biggie, they're close enough and work great. I get all the rated power out of them. The issue is that when I charge them up, they don't reach 100% at the same time. One battery...