    Issues finding a way to use a Ground Fault Interrupter on the PV side of my system

    Thank you everyone for your responses. I reached out to the manufacture (it was an MPP inverter) and turns out that since the PV side of the inverter is not galvanically isolated like the battery side, one cannot use an external ground fault device on the PV side. This means that the unit could...
  2. S

    Issues finding a way to use a Ground Fault Interrupter on the PV side of my system

    Hello all, Happy Friday! So currently I am trying to find a way to install a ground fault interrupter on the PV side of my system. Of course this is to remain compliant with NEC 690.41 , I have 2 strings and they are on my roof. My problem is that the inverter I am using states that it cannot...
  3. S

    How to wire a generator to an off-grid inverter that has relay contacts (NC, C, NO)

    This is the answer I was searching for. Thank you so much for taking the time to explain this.
  4. S

    How to wire a generator to an off-grid inverter that has relay contacts (NC, C, NO)

    Thank you so much for the response, I deeply appreciate it ?
  5. S

    How to wire a generator to an off-grid inverter that has relay contacts (NC, C, NO)

    Hello all, I have seem to have gone down the rabbit hole trying to figure this out. I have a PSW-H 3kW 120Vac 24V Phocos inverter. The inverter has relay contacts that of course will turn the generator on when the batteries reach a certain voltage and off when they reach a certain voltage. I am...
  6. S

    How to wire a generator to an off-grid inverter that has relay contacts (NC, C, NO)

    Hello all, I have seem to have gone down the rabbit hole trying to figure this out. I have a PSW-H 3kW 120Vac 24V Phocos inverter. The inverter has relay contacts that of course will turn the generator on when the batteries reach a certain voltage and off when they reach a certain voltage. I am...