Are my solar panels EOL

XO4001

New Member
Joined
Feb 13, 2021
Messages
185
Location
Bahamas
Having 48 panels in 4 string’s of each 12.

All panels in the same plane.
1641741984649.jpeg



The panels in front are the Chinese.

2 strings with Chinese 250 W panels 8years old.

2 strings with Peimar 300 W panels 4 years old.

Noticed that the Chinese panels is putting out real pour sometimes ¼ or ½ of the Peimar.

I expect that they would output 1/5 less but it is substantial more.

There are some snail trails on them but they suppose not the reason of less output.

Any ideas of what could be the reason or are they just End Of Live after 8 years.
 

Attachments

  • 12 am 1.jpg
    12 am 1.jpg
    299.6 KB · Views: 8
  • 12 am 2.jpg
    12 am 2.jpg
    302.2 KB · Views: 9
  • 10 am 1.jpg
    10 am 1.jpg
    235.4 KB · Views: 6
  • 10 am 2.jpg
    10 am 2.jpg
    240.3 KB · Views: 6
Last edited:
That is a lot of panels to check. Would take me hours One by one. 12 panels in series is more thanI feel comfortable with checking with my $25 multimeter.

Since thermal imaging has come down a lot and affordable by normal people and not just the world’s largest governments, I wonder if FLIR imagining would help with that:


3AC99644-3A4D-4D27-8AC3-B93EFDC955B8.jpeg
 
You need to test the Voc and Isc of each panel to answer this question. A single underperforming panel in a string will pull ALL panels in that string down to its level.
Thanks for your reply, just looked at how to test and will give this a try tomorrow if weather permitting.
 
That is a lot of panels to check. Would take me hours One by one. 12 panels in series is more thanI feel comfortable with checking with my $25 multimeter.

Since thermal imaging has come down a lot and affordable by normal people and not just the world’s largest governments, I wonder if FLIR imagining would help with that:


View attachment 78975
Thanks for the suggestion but I have no flir equipment in my toolkit, since the panels are ground mount I think it is not too troublesome to check them 1 by 1.
 
Do not disconnect any panels while the sun is shining. It would be very dangerous as well as it will destroy the connectors. You might be able to narrow down some problem panels/string with a DC clamp meter.
This is a grid tie system I presume?
Thanks, Im aware of the danger working with high voltage DC.
Planning to take 1 string out production and disconnect all panels from each other to perform the testing and hopefully I find the bad one or more.
Can you tell me more how I can narrow it down with a clamp meter?
And yes it's grid tied with zero feedback and battery's connected
 
I would think, while the system is up and running you might be able to test each string for starters with your DC clamp meter. Looks like you know which string is bad though, correct?
Once you isolate that string you need to find out the bad panel(s) in that string. Short of dismounting the panels you should be able to do a short circuit current test on each panel with a multimeter. I have MC-4 connectors with short lengths of PV wire still connected that I push the test lead points into to make it easy to connect to each panel. I have clipped off the parts of the connectors that lock together, making it easier to test multiple panels at a time. If you don't find a problem this way then you need to put a load inline with the test leads. Sometimes a short circuit test isn't enough to reveal problems without some kind of load.
 
I would think, while the system is up and running you might be able to test each string for starters with your DC clamp meter. Looks like you know which string is bad though, correct?
Yes I know exactly which is producing less, just changed 2 photos in my first post that were not correct.
Have to wait a couple days for testing because rain is expected coming days.
 
I'm going to guess by the voltage of the good panels that you have strings of 8 panels x3 per side, correct?
Hard to tell by the current but if you DO have 3 strings per side your current is low. Is this because you have zero backfeed and relatively full batteries? If there's nothing to consume power your system has to throttle back. Do you have any large loads you can turn on to see what happens to the incoming power?
 
No i'm having strings of 12 panels and 4 strings on 2 pc 5kW Deye inverters ( each inverter has 1 string good and 1 bad) batteries are 50% ( 4pc 16s 277ah) so basically i can use all i generate.
 
No i'm having strings of 12 panels and 4 strings on 2 pc 5kW Deye inverters ( each inverter has 1 string good and 1 bad) batteries are 50% ( 4pc 16s 277ah) so basically i can use all i generate.
OK I see those are 60 cell panels. Without counting I assumed they are 72 cell , which have higher voltage. Still less than 30 volts from 300 watt panels is pretty low. The lowest voltage string is only averaging 14 volts per panel. So you must have some panels putting out no voltage
 
Would a couple of incandescent light bulbs in parallel do the trick as a load?
Say 2 100W 115VAC bulbs at midday sun maybe I can find some in a store.
Or a halogen bulb.
 
Not sure if ac bulbs work with dc and a halogen or 200 watts of incandesent bulbs is too much load. A automotive headlight would work I understand. I have a gadget made with MC-4 fittings and a piece of Nichrome wire coil ( heater coil) that I use. If it gets screaming hot right away I know the panel passes the load test.:oops:Nichrome wire.jpg
 
Last edited:
A DC clamp ammeter is what you need. I have 40 panels, after installing them I checked them and found 2 that weren't producing, turned out to be due to bad MC4 connections which were easily fixed. Quick and easy to diagnose. You can get one for about $30 these days, just be careful it reads DC amps, many of the cheaper ones are AC amps only.
 
100W 120V incandescent will have Cold resistance of about 10 Ohms (hot resistance is higher, it is about 144 Ohms), you can check it with Ohm meter.
You should get DC Clamp-on meter as suggested, it is a great tool to have.
 
I have a DC clamp meter but was thinking that when you make a full short without resistor it will not give the correct reading in reference to voltage because that will collapse.
Do you not have to read both voltage and amps at the same time to find the condition of the panel?
 