herman2021
New Member
- Joined
- Dec 14, 2021
- Messages
- 10
I have a new Victron Multiplus 24V Compact and a new BigBattery 24V HAWK Lithium. When turning on the Multiplus it will go into Bulk Charging mode and make a hum for about 30-60 seconds then shut off completely. Another 30-60 seconds will go by and then it will turn on again and try again and shut off again. It will do this one or two more times and either a) keep going successfully, the hum gets quieter, and then eventually make it to Absorption mode or b) end in a Fault. I have a Cerbo GX and looked at the VRM logs and noticed "High DC Ripple" faults. Sometimes it says this in Victon Connect after it shuts off and other times it says nothing in Victon Connect... just that it is Off. I replaced the battery connections and feel pretty confident they are solid.
My Multiplus Charger settings are Current=50A, Absorption=29.2, Float=29.2 (29.2 was recommended in the HAWK "manual").
Any ideas?
Jeff
My Multiplus Charger settings are Current=50A, Absorption=29.2, Float=29.2 (29.2 was recommended in the HAWK "manual").
Any ideas?
Jeff