I keep blowing 400 amp t-fuses when charging at 240 amps

JedTheFed

New Member
Joined
Mar 2, 2021
Messages
48
Hello everyone,

Scenario

10 KW onan generator

cerbo gx set to accept 50 amps

800 amps renogy batteries

2 multiplus 3000 wires in split phase.

400 amp t fuse

I set both inverters to charge at 120 amps the 400 amp t-fuse blows. If I set them both to 100 amps charging it seems ok. Why is this happening?

I thought it was because my solar charger was on at the same time when the first fuse blew, but it is still happening. I was bringing the power up from 62% charge and it got as far as 71% before the last fuse blew. This time it even melted the fuse holder.

Can I not use the full 240 amps charging? It seems I could do this before but can not do it recently without the fuse blowing.

Why is 240 amps charging blowing a 400 amp fuse?

Gary
 
Than
Most common causes of premature fuse blow:

Bad connection at fuse that's generating heat.
Low quality cheap fuse that doesn't actually meet spec.
Thank you for your response. The t-fuses seem to be good quality and were tightened to inch pounds spec (i can’t recall what that was at the moment). I will definitely check that again.
 
Also what is the system topology?
Where is the fuse in relation to the batteries and the loads/charge sources?
 
Since the fuse holder melted at only 71% current its a heat issue caused by a connection with too much resistance.
The charge amps were a steady 230+ and the battery state of charge had climbed to 71% when the last one blew. I was definitely be checking the torque on the fuse next.

In another forum it was suggested it was just getting hot from being in a hot bay with the inverters, batteries and solar controller all together. Maybe my temp sense is not setup correctly.

Gary
 
Inch pounds on a 400? I would lean on it a bit harder. Polish the surface clean also.
Get your DC clamp ammeter on the fuse feeder to verify current.
 
It is a 400 amp tfuse slow blow fuse
Can you post a product link to it?
I've not seen a slow blow class t fuse and I went looking a few monthes back.
The demand for class-t fuses is high right now, as you have noticed many places are out of stock.
I wonder if some reject fuses got into the distribution channel so somebody could make a quick buck.
If the fuses are not blowing when the inverter/chargers power on then its not capacitor in-rush.
Is that what is happening?
 
Blue Sea chart says the T should pass about 2x rating for close to a minute.
Seems slow to me. I prefer to keep these a bit tight without worry of inrush or surge rating.

ClassT_Fuse.jpg
 
Can you post a product link to it?
I've not seen a slow blow class t fuse and I went looking a few monthes back.
The demand for class-t fuses is high right now, as you have noticed many places are out of stock.
I wonder if some reject fuses got into the distribution channel so somebody could make a quick buck.
If the fuses are not blowing when the inverter/chargers power on then its not capacitor in-rush.
Is that what is happening?
Go power 400 amp fuse. I blew 3 of them

 
Blue Sea chart says the T should pass about 2x rating for close to a minute.
Seems slow to me. I prefer to keep these a bit tight without worry of inrush or surge rating.

ClassT_Fuse.jpg
It does seem long and it was HOT! I am considering switching to a 400 amp breaker and tweaking the settings to slow down the surge.
 
What part of the fuse holder melted? Can you post a picture?
Where it melted was where the bolts go through the plastic. I tried removing the fuse while it was still smoking hot and this screwed up the plastic a bit. Its all back together and looks normal again until I replace it.
 