Solar house generator I started DIY back in 2000 - My path from Trace to Xantrex (on FLA battery) to XW Pro inverters on Tesla Model S batteries

Module #12 arrived from NewYork today

Modules #11 at 23v while #12 getting charged to 23v then will ready to hookup
this provides 60kwh @ 48v

20220922_111136.jpg
 
Last edited:
Anybody here have the Modbus Map aka table for the older ComBox fro Schneider ?
sorry I do not

I am a SW dude, but have never programmed on ModBus

So where/how is the best place to learn the programming model, etc for accessing ModBus?
With XW Pro soon to be ordered and anexisting Gateway I am part of the way there
python preferred
 
I got python talking thru modbus to xw pro with gateway
works with insight too
its just wanting to hold onto a ComBox path to an older xw4548
I have never gotten the xw pro to work right with generator assisting. So i use the xw4548 from ac2 to charge my batt bank
write if you want more
 
I got python talking thru modbus to xw pro with gateway
works with insight too
its just wanting to hold onto a ComBox path to an older xw4548
I have never gotten the xw pro to work right with generator assisting. So i use the xw4548 from ac2 to charge my batt bank
write if you want more
any specific python libs?
 
solar[3] = solarDev = ov_modbus.session('192.168.1.91',pollinterval=3,unit_id=1) # port=502 GATEWAY
solarDev.num = solarnum
sensor = ov_modbus.sensor(solarDev, 40278, 1, signed=False, divisor=100) # 40278 DC Bus Voltage
sensors['XW_DC_E'] = sensor

the above works on gateway but the below does not work with ComBox

solar[2] = solarDev = ov_modbus.session('192.168.1.92',pollinterval=3,unit_id=1) # port=502 COMBOX
solarDev.num = solarnum
sensor = ov_modbus.sensor(solarDev, 40278, 1, signed=False, divisor=100) # 40278 DC Bus Voltage
sensors['XW4548_DC_E'] = sensor
 
solar[3] = solarDev = ov_modbus.session('192.168.1.91',pollinterval=3,unit_id=1) # port=502 GATEWAY
solarDev.num = solarnum
sensor = ov_modbus.sensor(solarDev, 40278, 1, signed=False, divisor=100) # 40278 DC Bus Voltage
sensors['XW_DC_E'] = sensor

the above works on gateway but the below does not work with ComBox

solar[2] = solarDev = ov_modbus.session('192.168.1.92',pollinterval=3,unit_id=1) # port=502 COMBOX
solarDev.num = solarnum
sensor = ov_modbus.sensor(solarDev, 40278, 1, signed=False, divisor=100) # 40278 DC Bus Voltage
sensors['XW4548_DC_E'] = sensor

I also saw you posted:

I think that happened
my geek son makes the ov_modbus stuff for me and it error'ed today

now it won't sell

so your son has created a python library for modbus, with 'ov_modbus' as the prefix.
Is it private or open source library?

I see there are several different python libraries for ModBus.
I have no idea the merits of them.
Again I do not yet understand the Modbus model well yet, let alone the Schneider Maps, etc
 
My Conext PDP (Power Distribution Panel) for the XW Pro arrived today

On the table in its box

20220929_121041.jpg

64 lbs

good packing

20220929_121047.jpg


shipping package removed.
the Tall box is 31 inches tall

20220929_121413.jpg

door open



20220929_121434.jpg

row for AC breakers - supporting 3 inverters

20220929_121515.jpg

room for 3 250a breakers on the right of this row
along with 8 breakers for 4 charge controllers (60 amps prior to and 80 amps after each charge controller)

20220929_121521.jpg

set of 3 60 amp AC breaks with interlock for AC IN and AC OUT

20220929_121535.jpg

This how the layout will be, PDP on the right, Conduit Box under the forth coming XW Pro

Wall plate and surge protector (extra) plate, and misc

20220929_121650.jpg

And finally where the PDP will be hung, upper right of of pic, replacing those 4 breakers shown
20220929_122739.jpg
 
Last edited:
Looking good, the Sch stuff does for sure look sexy, even in the back of a crappy travel trailer.. overkill? yes...... and great performance.

Victron Multiplus Quattro Comparison Chart.jpg

1664487611797.jpeg
 
Here in Florida, after the hurricane. No utility power.
Cannot get more than 500 watts of charge from AC2 (gen) into my batteries. Any ideas ?
Gen will automatically provide the house loads power plus 500 watts more for charging. But when my loads go down, I still cannot see more than the 500 w into batteries. When I have grid ac1 before the storm, I could charge 2 to 3 kw's.
 
When I try my older xw4548 it refuses to qualify the ac2 generator. The Combox webpage show AC2 voltages at 105/108 and together at 213v. Yet it says 0 Hz for freq. And always Qualifying, never Q-- good. And yet it worked ok a month ago.
 
When I try my older xw4548 it refuses to qualify the ac2 generator. The Combox webpage show AC2 voltages at 105/108 and together at 213v. Yet it says 0 Hz for freq. And always Qualifying, never Q-- good. And yet it worked ok a month ago.
The day and time to test your system was yesterday, sorry.
 
@Jennifer

Wondering if you noticed the title change?
also added a Table of Contents fast link to various subjects in the thread in POST #1

if there is a subject or post you think should be in the ToC, please tell me
man, this is getting good now, it has been a fun journey
 
Here in Florida, after the hurricane. No utility power.
Cannot get more than 500 watts of charge from AC2 (gen) into my batteries. Any ideas ?
Gen will automatically provide the house loads power plus 500 watts more for charging. But when my loads go down, I still cannot see more than the 500 w into batteries. When I have grid ac1 before the storm, I could charge 2 to 3 kw's.

I would start a new thread to increase visibility to the forum.

Sorry I can’t offer any further help.
 
Looking good, the Sch stuff does for sure look sexy, even in the back of a crappy travel trailer.. overkill? yes...... and great performance.

That does look great ! My SW4048 isn’t mounted half as nicely.

And IIRC your trailer is quite nice, under a shade structure of solar panels ?
 
Possibly a boring post today, but I spent some time on an upgrade, and I give some advice as to how to avoid the issues I went through


Back when my future wife bought this house in 1994 (built in 1930, addition in 1947) it had the old style wiring - Knob and tube wiring:


img-knob-tube-e1560276052755.jpg

and almost all of the insulation had degraded and fallen off of the wire, leaving BARE wires throughout the house. Also the entire house was wired with just 4 circuits, protected by 4 fuses. OH MY. She and her son began the process of adding Romex wiring to boxes, etc, etc but didn't touch the fuse box

In 1995-1996 I came along and I began the task to swap out the fuse box and add a proper service entrance panel with meter base. Got the permit to do so. I got the "approved" plans and installed the service entrance and ran the SER wire from it to the fuse box area, getting ready to swap out the fuse box with a new Square D service panel.

First mistake I know I did: I should have put in a 24 (or bigger) breaker panel and not a Main Grid 12 breaker panel. Main breaker was 125 amp.
Second mistake: Should have done a 150amp main - oh well

Here is the then "new" service panel:

20221002_134735.jpg

upper right 2 pole 40amp breakers goes to the oven in the kitchen
upper right 2 pole 30amp breaker goes to water heater receptical - no connected, using gas and PV to heat water
lower right 2 pole 60amp breaker goes to Solar Generator system and then to the main Critical Loads Panel (CLP) located downstairs in the basement.

Notice that all the 1 pole breakers are off, no circuits are presently connected to them.

NOTE: I could put in a 2 pole breaker here for a NEMA 14-50 receptical for an EV charge port someday, for GRID powered charging

Below is the main CLP in the basement (from a few weeks ago when I swapped out the BYPASS switch)

20220910_201830.jpg

From the above Main CLP, there are 2 breakers on the lowest row, one (lower right) to a Sub CLP located below the Grid Service Panel and another (lower left) to a Sub CLP located in an out building.


Okay now to the work I did yesterday. When I installed these CLPs back in 2000 with the original solar system, I only ran 1 L1 power leg, since I only had a 120v inverter

Third mistake: should have run both L1 and L2 even when I would NOT use the L2 leg for twenty years

So to fix that, I ran the L2 wire through the conduit yesterday from the Main CLP to the house Sub CLP

From the Main CLP: (the black wire is the new one on the lower right breaker)

20221002_134817.jpg

down to the raceway:

20221002_134837.jpg

and up to the larger junction box, which is connected to the through the wall 2" conduit leading into the crawspace. From there conduit in crawspace comes up under the Sub CLP

20221002_134829.jpg

as shown here in the center conduit entrance in the Sub CLP:

20221002_134629.jpg

which then is connected to power that Sub CLP as shown here:

The RED wire was already installed, while the BLACK wire was installed yesterday:

20221002_142056.jpg

NOTICE: On the right side of the panel, is the "pass through" circuit that goes from the above Grid panel's 60 amp breaker thru this Sub CLP and carried in the conduit on the right, down to the basement connection. When I built it, that seemed the best way, but don't know if it "valid".

That was upgraded from 1 L1 leg to 2 legs, with the new L2 leg recently as well.


I expected the job to take 4 to 5 hours. It took 10 hours

Well, I am getting old and crawling multiple times into and out of the crawl space, inserting the fish line and pull wire took its toll and I rested many times - lol.

I admit I did remove the old conduit in the prior picture and that took time to do it right, extracting some length of the 3 wires and then re-pulling the 4 wires that last 6 feet back to the Sub CLP


So, my advice is to do the following:

Plan bigger than current requirements
even when pulling wire for 120v, pull 2 legs, L1 and L2
Maybe I should have used 1-1/4" conduit instead of the 1" I did
Install larger service panels than you think you need

When building a new home, Install the Main Grid Service Panel but also install a secondary Critical Loads Service Panel with most of the house circuits to this CLP - this allows for the addition of a solar generator between the two later if not immediately

Adding a new solar whole house generator to an existing house without such, makes things more difficult as most times there is not space to put the CLP and extending circuits is hard. In my existing house I upgrade I failed to do so as I was not yet Solar aware. That is why my Main CLP is in the basement and the Sub CLP is back up near the Grid Service Panel

as of today, my body hurts - time for another nap today
 
Last edited:
Possibly a boring post today, but I spent some time on an upgrade, and I give some advice as to how to avoid the issues I went through


Back when my future wife bought this house in 1994 (built in 1930, addition in 1947) it had the old style wiring - Knob and tube wiring:
*Shudder*
Good work in getting rid of the knob and tube, looks like great progress!
 