  1. A

    Will generator work with Growatt?

    Assuming Lipo4 from the low voltage numbers. Output Voltage from the two charge sources would need to be very close. I had two SCC charging batteries if output voltage was 0.1 volt different the lower one moved no amps. Other than that should work fine. I have charged with two SCC and generator...
  2. A

    Low temperature cutoff options when your bms and charge controller don’t.

    Don’t jump in with both feet others may advise against but I think if you had a single pole open on fall thermostat of some kind and broke a sensor wire it would disconnect. You may be just wanting to stop change but allow discharge, I don’t know how to do that.
  3. A

    Ampinvt 80A Controller set up?

    So I have the 12V 120-3000 also have two 60 amp SCC by another name but the same. The inverter yes like a power supply. You can manually change the current and voltage but that is it. The SCC even on fla just 1 voltage no float no absorb I put them on the shelf and got a growatt.
  4. A

    How serious is ventilation design with FLA?

    Please don’t use PVC air moving though it cause static buildup. You are producing oxygen and hydrogen and now you can produce a spark, extant! I have a cabinet shop ( hobby) originally I used PVC for dust removal. WITHOUT MATERIAL MOVING THROUGH IT. It would very quickly build up static and it...
  5. A

    Possibly dumb questions from a newbie

    I live North of Russellville. I have a DIY grid tied system on Entergy of Arkansas. I have a 25 year 1 to 1 contract. I have a Schneider XW6848 and two of their solar charge controllers. I purchased panels, batteries, and Schneider gear from Northern Arizona wind and Sun. Great company. I got it...
  6. A

    Problem with inverter and DC overcharge

    Inverter enabled not in standby? Bypass breaker in correct position?
  7. A

    Problem with inverter and DC overcharge

    You need to become a lot more familiar with your system. Off grid is not a set and forgot. That being said, you have two methods of charge. One being the charger in the inverter, the other the solar panels through the charge controller. Both have settings that can be configured to the battery...
  8. A

    Big systems, how big is big? Biggest?

    I started by reducing load! 6.1 kw panels 42 kw fla batteries 6.8 kw Schneider Sell to Grid connected 1 to 1 contract About 3 kw surplus annually
  9. A

    Panel upgrade

    I would unwire panels and short circuit and check panel output that way. If watts check out that way. Look at wire size and length.
  10. A

    Panel upgrade

    Are creating a 2 nd charge circuit? Or combining new and old panels to create a single charge circuit? Panel voltage is easy to produce but much cloud of shading can cause amps to fall off bad.
  11. A

    Batteries dead suddenly

    What method do you use to determine approximate SOC? The system could have been lower than you think it was.
  12. A

    Batteries dead suddenly

    Looking at SOK specs they won’t charge under temperature, doesn’t say won’t discharge.
  13. A

    Batteries dead suddenly

    If off on low voltage charging should wake them up. The b2b charge is the only source of charge? What amperage is it capable of? Do you have cables large enough to support the amps? How long and often have you been charging?
  14. A

    Batteries dead suddenly

    If temperature recovered and BMS is still open l would think that they are off on low voltage disconnect. Do they have internal heat? If so it could have contributed to running them down.
  15. A

    Batteries dead suddenly

    If SOKs have built in low temperature cut off on the BMS that could be what caused the 1 with 2.4 volts to disconnect. Were the batteries allowed to go to 0 C. ? If not could be they weren’t charging because of low temperature.
  16. A

    Shed Solar - See any mistakes?

    Ok I’ll bite, 60amp battery fuse x 50 volts is 3000 watts. Is that all the 5000 growatt is? Or do we need a upgrade there?
  17. A

    24V wiring diagram help

    With having 5 outgoing DC circuits I would look at a DC breaker panel and forget all the fuses. Schneider, Midnite Solar, or similar. Resettable and means of disconnect for everything.
  18. A

    LFP Battery Rest Period After Discharging before Recharging?

    Just last night my mobile system ran at 0.09C my 24 volt 280AH pack didn’t raise 1 deg F. It did raised 2 deg F. Recharging today though.
  19. A

    24V wiring diagram help

    ATXist brought up a good point. Also 620 watts of panels if flat mounted is small fo a growatt. My personal experience it’s self consumption is about 1.25 kw per day. Of corse if you turn it off or get the power save to work for you ( most don’t) then it would be great.
  20. A

    LFP Battery Rest Period After Discharging before Recharging?

    Unless my calculations are wrong that is an average discharge of 0.1C. That C rate should not raise the pack temperature any more than changing would so I see no reason to “rest” before recharging. Besides unless you have east facing panels, battery will get a break from discharge while panels...
  21. A

    Need help understanding solar panel connectors, saftey

    Sae would be good if you were tearing down and moving weekly but for the long term use you can get some corrosion that would result in voltage drop. I would replace all of them with mc4s. The ones I got from Amazon look as good as any I have seen. Be sure to get the recommended crimper.
  22. A

    is the optimum year round angle what you really think it is?

    I am in Arkansas as well. I agree with your line of thinking but, it would also depend on what season you need more kw’s. If you burn wood say and need lots of a/c. I have a homemade single axis ground mount with 6.1 kw on it. I have them at 15 deg from horizontal in mid summer. Currently 60 deg...
  23. A

    Here's my plan to install a 230V Mini-Split

    On your drawing it looks like you plan to run a 3000 watt at 12 volts inverter with #2 awg? That is a lot of amps. If you are not planning to use the whole 3000 why not leave the xantrax? Or maybe I am wrong and it is 24 volt. It is still marginal at that.
  24. A

    Advice on Big Battery shutdown issue. Is my design at fault?

    I haven’t tried the power saving mode yet. But idle consumption with no load is around 55 watts times twenty four hours is 1.32 kw per day. That could be a larger part of your battery consumption than you are figuring with winter sun.
  25. A

    Advice on Big Battery shutdown issue. Is my design at fault?

    Please keep in mind if you are inverting 27-7 with the growatt my personal analysis is it will self consume 1.25 kw. 1 kw of panels flat and winter sun could be that low of production.
  26. A

    Reverse Polarity RV Plug on Bluetti/Ecoflow/Goalzero?? Is this a problem?

    Once I installed an inverter in a RV that was wired that way. It was tripping the internal breaker. It took a while but I found a plug that had the bare ground touching the neutral screw but with one reverse polarity I would have never had a clue.
  27. A

    Cable Sizes

    Awg 2 carrying 190 amps is from the free air chart. In free air has to be where conductors are installed so that heat can disapate. Can’t touch insulation or building materials. Connectors also need to be rated for that temperature rating. Also the disapated heat can’t raise the surrounding...
  28. A

    24v single cell low temp cut off

    2S is = to 1 24 volt battery. So any interruption in that series connections and both batteries and not providing power. The other parallel battery set would be required to carry the load. If it is not capable of carrying total amps it to would be taken out. Back at the first to open bms from...
  29. A

    Power draw problems

    The numbers are off a little 1500 watts / 10.7 volts = 140 amps x 1.1 90% efficiency = 154 battery amps. I would look at connections and wire size.
  30. A

    24v single cell low temp cut off

    What voltage is each battery. Are they 12 volt connected 2S2P?
  31. A

    Need help and a little direction

    Are you saying the OP can’t series the four SOK’s without some balancing device? What would that look like?
  32. A

    Water heating, in a vehicle

    So if you reduce the engine heat by much you will affect the mpg. Using a alternator requires horsepower. Like running A/C cost mpg. Or is it redundant you want? I once built a heat exchanger to heat water entering water heater. It captured heat from the shower drain. My self built RV I used...
  33. A

    Need help and a little direction

    That sounds doable you can give me a call 479-968-2266
  34. A

    First time mounting (solar panels)

    I wouldn’t consider not using a racking system. I have used Tanarack but not on a shingle roof. If not what is the alternative Z brackets? If so how would you probably seal that? How much debris would build up at the top and under neath holding moisture and shorting the life of the roof...