  1. M

    SOROTEC REVO II 5.5k power consumption is weird, help!

    Do you há é AC charging on with 10 amps? Or it is off? From my experience, if you dont have a relativa calibration made the AC numbers Will never BE real. You have to calibrate the PV and the battery to bê acurate. Those numbers Will give a acurate AC reading ( bether one instead of the fake...
  2. M

    SOROTEC REVO II 5.5KW Battery Bulk/Float Charging Setup

    My JKBms died to read to cells, so i installed a seplos BMS. So far it is working great with can bus with the inverter. The only downside is the balance current is 150ma but the features that this bms has are massive. The bms send info to the inverter and lowers the charging current when is...
  3. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    Hi, No. I can only read setting. to change is only possible in the inverter screen. This if was given from sorotec.
  4. M

    EASun 5KW inverter draining battery in hybrid mode

    The inverter uses the battery as power source if battery is available. My BMS, In AC mode , reads 0.77A all night. This is how this inverter works. it seams that idle consumption will came from battery and maybe a part also from the grid.
  5. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    Grid limiter will only work with the external CT, and the correct operating mode. The PV must be arround 350volts. I never got it to work consistently without a battery conected, but i found if you enable AC charge of battery it will be more consistent. I also read that the load must be arround...
  6. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    No. the 5.5kw is the max operating AC power. You can peak that but only for a few second till the inverter shuts down. for 7.5kw you hate to parallel 2 units, to 11kw. ( must be the same software version or the parallel will not work.
  7. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    No 11000wats it the peak ac power for a very limited amout of time.
  8. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    No. This inverter doesnt allow any modifications by software. it must be done in the touch screen.
  9. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    You cant change any parameters in yhe software. Only in the touch screen.
  10. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    I will try to make it tomorrow in the holliday here. you can adjust some things like PV voltage and PV amps ( you will need a multimeter and clamp to mesure amps. ) When you adjust the battery amps and voltage you will get correct grid power. The only down side, in my case is that i lost float...
  11. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    sorry for my lack of time. I try to make the video tomorrow how to calibrate. Be ware that when i made the calibration perfect the inverter would do float. maybe in your it will, i dont know. In mine i belive that it has to be a amp diference in the battery amp display to the float work. Mine is...
  12. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    Try contact sorotec power. I believe they can sell you the display.
  13. M

    Heltec (JK) 200A Smart BMS with 2A Active Balance

    Yes a see my amps reducing, but in my inverter i select 57 amps and it only stops at 58,but this is a inverter problem, not bms. The bms doesnt regulate amps, it only protect the battery for overvoltage and under voltage in the cells. The inverter must regulate the charging.
  14. M

    Heltec (JK) 200A Smart BMS with 2A Active Balance

    Check if your inverter as any calibration for the AC voltage and amps.
  15. M

    Heltec (JK) 200A Smart BMS with 2A Active Balance

    Use a multimeter and measure the voltage of the pack. Then use the voltage calibration on the bms setting and insert the correct voltage of the pack. Then you should be ok. After calibration, measure every cell voltage to see if it matches what the bms reports.
  16. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    I will make a video and give you instructions how to do the calibration. For me the correct values for charge and discharge, stopped the floating from working. The values were all correct as measured by multimeter.
  17. M

    Best PV Array Settings?

    Yes i will be loosing some power but in winter i will never get full optimal PV conditions, so i will get max available power. In the summer the 4500W are more than i can store and use during the day. At this time i use 12kw a day, and the PV produces 30kw daily. I have the batterie always full...
  18. M

    Best PV Array Settings?

    The recomended operating range is from 120volts to 450volts . The max is 500VOC. My problem may be that the max amp of the mppt is 20 amps and 5P2S will be 23amps in open circuit and 21 amps operating. This can kill my mppt charger? ou it will just limit the current to 20amps?
  19. M

    Best PV Array Settings?

    Hi, i wondering what is the best config for my PV array, especially during winter. I have 10 445W solar panels, that combined give me 4500W with 10amps and 450volts on a series array. This is at max of the operating range VOC on the inverter. Should i switch to 2 series one parallel string...
  20. M

    Earthing of panels

    Yes 2 SPD of 2 poles, one for each string. About earthing, i would get one earth pole for the metal structure, panels suports and panels. That can be mixed with the earth from the SPD's, on a earth connection box. That earth pole spaced at leat 3m from the existing ones.
  21. M

    Earthing of panels

    Here some info on the subject. https://www.solarpowerworldonline.com/2018/10/lightning-and-overvoltages-why-solar-systems-need-surge-protection/ You will find many more online.
  22. M

    Earthing of panels

    The one you show me is for AC voltage, not DC. It must be DC for solar arrays. You can use use one for each string, then send them for the same earth pole. Remember do not mix you house/inverter earth with structural/panels/SPD earth. I boughy mine here - https://a.aliexpress.com/_msmMFHJ
  23. M

    Earthing of panels

    Yes, you conect the positive to one side and the negative to the other. The earth is in yhe lower side. This is a parallel conection to the PV wires. When you have a surge in any of the array wires, like 10kA, the device will send that voltage and amps to earth. In that case, the visors will go...
  24. M

    Earthing of panels

    You should earth the structure and every panel, in the hole marker as earth. The rest of the panel doesn't have continuity, so it is to place the earth wire in the designated hole. If you drill, then it is not needed to be in that position. The wires, should go directly to the earth box and to a...
  25. M

    Help With REVO II VE 5.5kw - CT Function

    JK BMS Website This is the one i bought - https://pt.aliexpress.com/item/4000529723243.html?spm=a2g0s.9042311.0.0.67feb90afnC2tU It is very good and it as 2 amp balancer integrated. There is a similar one that is Heltec BMS With Jblance software you can import all data to graphana and...
  26. M

    Help With REVO II VE 5.5kw - CT Function

    In your comment you say LIFEPO4 can be overcharged at 4.2 - Don't you mean LIthium LI-ION? Every specs say max voltage of 3,65 for LifePO4. At 54.4 you are at 99,8% battery max is 58.4 if you have a perfectly balanced pack. I don't charge mine more that 56volts, there is no point in stressing...
  27. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    Yes, i have my PV ground separate from the Home and Inverter. I already add a discussion on my youtube video with #Averagejoe about it. I said that all ground should be connected to the same point but i said to him the same you are telling me and what i have done in my setup about grounding, for...
  28. M

    Help With REVO II VE 5.5kw - CT Function

    Well, Today the battery settings worked as expected. I set the bulk at 55.2 and it stopped there. Great. The float voltage also kicked in at 54 as set, so also great. Maybe it was like you said. You need to reboot the inverter every time you need to set the changes. Should not be necessary, but...
  29. M

    Heltec (JK) 200A Smart BMS with 2A Active Balance

    It is only a shame that this BMS CAN port can be connected to the inverter. I don't know why every manufacturer uses a different communication protocol for CAN port.
  30. M

    Help With REVO II VE 5.5kw - CT Function

    what i mean is specs vs reality. In mentions CT limiting function with external CT - This is reported with several users, that this only works if you have a PV voltage around 300volts. If the inverter specs say that you can have to 500volts array, it should works in any voltage on the range...
  31. M

    Revo II tripping breakers when 2 or more are in use

    OK, the Mppt version is the same as mine. The inverter is older than mine. PM me with the details and firmware. i give it a go. :). If you can show me what was the J-link you bought i appreciate it. I see many different ones online, like mini and other. The original one is 500dol..... I don't...
  32. M

    Sorotec REVO II 5,5Kw / EASUN( AXPERT/POWLAND) IGRID VE II 5,5KW

    From the pictures you have max out the PV capability, since it is displaying more than 5000W in the PV array. I should have divided that power to several REVOS, not only in one. If you are solar only, not battery, the inverter will give as much power as the PV can supply and you are exceeding...
  33. M

    Revo II tripping breakers when 2 or more are in use

    How did you update your Firmware? I asked for it at Sorotec but they refuse to give me. I have to pay for shipping to get a new controler board with the newest firmware. Can you give me the steps for flashing, what software did you use and the firmware file and its version? my mppt version is...