  1. M

    How would I go about building a 204.8 LFP battery pack?

    The existing AC chrged could be fed after the rectification with 240 VDC from the PV, there would need to be some form of regulation to avoid over voltage conditions. Working with oddball equipment can be challenging due to lack of off the shelf components, there is always a solution with...
  2. M

    How would I go about building a 204.8 LFP battery pack?

    The UPS would have a charger, assuming maximum charging voltage is 230.4V (14.4 per 12V nominal ) that would be slightly high for 60 cells, 67 cells using 230.4V would charge to a maximum 3.44 volts per cell.
  3. M

    How would I go about building a 204.8 LFP battery pack?

    Use 60 LFP cells of desired capacity in series with a 60S BMS ?
  4. M

    Hello everyone, sorry I'm late! I have a nickel iron battery bank but cannot find a suitable inverter.

    My experience with NIFE is extensive in railway signaling applications, some had been in service for over 30 years with electrolyte replacement every 3 years, despite that they wouldn't be my first choice, they are too inefficient in my opinion. Current technology such as LiFePo4 is far...
  5. M

    Hello everyone, sorry I'm late! I have a nickel iron battery bank but cannot find a suitable inverter.

    NIFE are extremely robust, long lasting at the expense of being inefficient, compared to other chemistries, including LA, they can be refreshed with anelectrolyte change and last for decades. There is equipment which can be programmed to accommodate their requirements, see above, they never...
  6. M

    Hello everyone, sorry I'm late! I have a nickel iron battery bank but cannot find a suitable inverter.

    There is equipment that can work with NIFE battery banks, they have custom settings which allow for the large voltage swings, they do however tend to be more costly, furthermore there are inverters which can interact with the grid programmable to incorporate various functions including AC...
  7. M

    Does an alternator fully charge a lead acid leisure battery?

    Automotive alternators are designed to recharge a healthy lead acid battery briefly after starting along with being able to support the lighting, ventilation and other loads applicable to the vehicles operation. Whilst it is possible to charge auxillary batteries it will reduce the alternators...
  8. M

    Maximum series fuse rating

    Overcurrent protection is specifically sized to protect the conductors, not the devices connected, therefore use the appropriate fuse as specified on the modules, it's to protect the attached conductors. Any overcurrent should be sized to protect the minimum gauge utilized within a given...
  9. M

    Off grid system advice

    As it appears there is a generator available, my suggestion would be to measure the kWh requirements with a recording device to establish a baseline of the energy required for the intended usage. Attempting to guesstimate using specifications is difficult due to unknown duty cycles of the...
  10. M

    1amp +/- Charging Diff Between 2 Parallel 8s Packs ~ Should I Tweek It

    Yes, I haven't been on NAWS forum in a while, seemed to become stagnated on lead acid with LFP being referred to as not suitable for DIY, here its the other way around and since I would never consider LA again this environment is more suitable.
  11. M

    1amp +/- Charging Diff Between 2 Parallel 8s Packs ~ Should I Tweek It

    Measure the voltage drop across the cables of each battery independently with a fixed load, that will determine if the cables are within close proximity to one another, measuring resistance without load is not dynamic, current draw will reveal any high resistance terminations.
  12. M

    got sparked when connect mppt to battery, bad??

    The SCC takes it power from the battery, personally I use a disconnect to isolate so a spark, if any, would not be seen. What are you referring to, a small spark or large, a SCC is considered an extremely light load but a load none the less, so a small spark may be possible.
  13. M

    got sparked when connect mppt to battery, bad??

    Did you by any chance have an inverter connected? Even turned off the capacitors will cause a spark on initial connection.
  14. M

    What about an 8s 4p 24V configuration?

    My first build was a 4P 8S pack with 100Ah cells , it's been in service for 3 years without any problems, the cell blocks remain in ballance even when fully charged, which is not done on a regular basis, normally a lower value is used, ~90%, initially top ballanced. Whilst I understand the...
  15. M

    Panel voltage

    The answer depends on the controller being used, with PWM 12V nominal panels would be required, MPPT on the other hand needs higher voltage so 24V nominal panels would be used.
  16. M

    Welded vs. bolted busbars

    The association with cell failure in lead acid is not something to be over concerned with when using LiFePo4, as the cells do not fluctuate in voltage, as is the case with lead acid , where a single cells failure can be masked by the ballance of cells working harder. When using a BMS, any...
  17. M

    PWM CHARGE CONTROLLER

    There are many types of PWM controllers, from simple cheap versions to more professional and everything in between. The cheap ones have a target voltage, usually 2.4V per cell or 14.4V for 12V nominal, when that value is reached it resorts to push width modulation (PWM), a switching off and on...
  18. M

    Chargery BMS, DCC (Solid State Contactor) thread.

    MOSFETs typically have around a voltage drop of ~0.6V, being they are semiconductors, not conductors, hense the cooling fan, the higher the current the greater the losses, in the case of a 100A load at 0.44V.drop, the loss would be 44W, or 3.35%. At lower current the losses would naturally be...
  19. M

    Fuse Insertion

    The current is shared equally in a parrallel circuit, therefore the fuse would need to be connected to both positive wires however it would be better to fuse each with an appropriately rated fuse.
  20. M

    Mini Split Help

    Don't use a modified sine wave, the compressor motor will overheat likely causing premature failure.
  21. M

    Mini Split Help

    There needs to be a load calculation done, the best way would be to use an alternate source, grid or generator, using a power monitoring device like a Kill a Watt in real use over the time required. Doing an estimate using the rated wattage is inaccurate because there are too many variables...
  22. M

    Mini Split Help

    Having 5 12V 100Ah batteries would suggest a 12V nominal system, if the split uses 6.5A @ 230V the current on the DC side would be approximately 130A, but inrush during initial start will be double or more, which will cause significantl voltage drops, hense the low power fault. Without going...
  23. M

    I need a new inverter

    Outback 2012 MT will do the job but will liberate you of ~$2000
  24. M

    Use vehicle chassis as inverter negative conductor? Pros/Cons

    Using a secondary deep cycle battery dedicated for the inverter is by far the better way to go, almost 80% of vehicular breakdowns are electrically related, 80% of the electrical problems are chassis negative bonding related, having a potential 100A draw seeking the party of lowest resistance...
  25. M

    Use vehicle chassis as inverter negative conductor? Pros/Cons

    Personally I would never use the chassis as the negative and secondly I wouldn't use the starting battery to feed an inverter for anything other than short duration use as the battery nor the chassis intended or designed for the purpose.
  26. M

    48 volt charging 24 volt battery with SCC

    Some controllers allow battery to battery charging, Morningstar TS MPPT is one example, as it can be programmed to limit current flow. Batteries have high current potential which would likely cause the controller to run at maximum capacity continuously ifthe battery being charged is deeply...
  27. M

    Powmr 3kw off grid inverter questions- Cant get over 1kw production- Weird/

    Ignorance is not stupidity, stupidity is doing the same thing repetitively expecting different results, we all learn from others experiences, failures along with success, I'm not intentionally being confrontational, just pointing out the difference between the two.
  28. M

    Powmr 3kw off grid inverter questions- Cant get over 1kw production- Weird/

    Having a single SCC rated to handle all the charging is the best approach but also more expensive, having 2 charging sources is possible if the settings of both chargers of are identical, not always possible though, if not customizable. This is why many serious operators generally stay away...
  29. M

    Powmr 3kw off grid inverter questions- Cant get over 1kw production- Weird/

    The inverters ability to support loads directly from PV is limited to its on board MPPT's capacity, in your situation around 900W, any more is taken from the battery, the problem is the battery will never get charged if output exceeds input. Having a separate higher capacity SCC also...
  30. M

    Powmr 3kw off grid inverter questions- Cant get over 1kw production- Weird/

    To get around the problem I would remove one array string and use a separate charge controller set to the same parameters as the inverter MPPT, or use a separate SCC with a higher capacity as the sole controller. The thing to remember is any loads will subtract from the charging current, if...
  31. M

    Powmr 3kw off grid inverter questions- Cant get over 1kw production- Weird/

    Looking at the specs the Plus version has a 60A MPPT charger, the regular is 40A, if this is correct then the nominal output would be 960W, this would be consistent with your observations, the MPPT charger would be over paneled but cannot exceed it's maximum capacity. This is benificial during...
  32. M

    Sw 4024 not inverting from 115ah lead, passes ac from Honda eu2000i. Two weeks no power,off-grid 40 years

    Unfortunately without being able to gain insight with the devices needed, it's extremely difficult to diagnose the potential problems, it's approaching the system blind, it is unfortunate that there is no direct visual interface, To add insult to injury, the product is at it's end of support...
  33. M

    Powmr 3kw off grid inverter questions- Cant get over 1kw production- Weird/

    At 26.8V a lead acid battery is close to being fully charged, hense the reduced current, or wattage, discharge the battery to a lower voltage and see what happens, more than likely it will increase, but this isn't necessarily the case if the conductors are sized on the smaller end of the...
  34. M

    Daly 250A, current (amperage) reading jumping/inaccurate/inconsistent

    Even high voltage transmission lines, 500 000V use regular transposition points to cancel out magnetically induced interference, both in AC and DC, if the inverter is actually taking intermittent bites out of the battery there would be a rising and collapsing magnetic field, because the...
  35. M

    Daly 250A, current (amperage) reading jumping/inaccurate/inconsistent

    Twisting the cables can reduce noise or ripple by cancelling superimposed signals, this is used in telephony to reduce cross talk as well a anti side ton induction coils for filtering, at least that is what was done before cellular phones, it is also used in computer cables. Google ripple and...