  1. K

    Solar configuration

    Ok, great. Thank you! Where can I find a reliable wire rating chart? Is this reliable? So wire size for 182,2A is 00awg (67,4mm2) wire?
  2. K

    Solar configuration

    I see. So for sizing for the 182.2A DC input listed: Is it correct that 4awg (25mm2) 7feet wire can handle 150-200A? And together with 4awg wire I should use a 180A circuit breaker?
  3. K

    Solar configuration

    Ok. Not size for the 120A DC output listed?
  4. K

    Solar configuration

    Thank you very much! 😊 How to determine wire size and circuit breaker between inverter and battery? My battery is 48V 270ah (13kwh) Here is the inverter:
  5. K

    Solar configuration

    Ok. But according to your "1.25X the wire rating" statement I should have a 25A breaker when using a 13awg wire which is good for 20A? This is for protecting the wire?
  6. K

    Solar configuration

    Ok nice. I've already a 2.5mm (13awg) wire buried from the garage to the battery shed. What about my 63A circuit breaker, is it pointless to use?
  7. K

    Solar configuration

    Ok, I've bought a 63A breaker, it's maybe too big? Wiresize: is this correct?: I have 6S 230w panels. 230x6=1380w Vmp=30v so 1380/(30x6) = 1380/180=7.66A So I have to use a wire that's good for 7.66A? 1.5mm2 (15awg) wire is good for 15A so it should adequate?
  8. K

    Solar configuration

    Where is the "max fuse" value on this? Should it be listed here?
  9. K

    Solar configuration

    Ok, thank you, then I'll go for 6S Ok, no fuse in 6S configuration. Anyway I want a breaker to cut the power if I want to. What size circuit breaker do I need before the inverter? Ok, so strings is the same as parallel.
  10. K

    Solar configuration

    The same with this inverter? I have a Voltronic Max 8kw. Is it possible to have 3s2p? It's often shading on three of the panels... And what size circuit breaker? I assume I don't have to fuse the panels in 3s2p configuration? I don't understand the manual with the recommended solar panel...
  11. K

    Solar configuration

    I have 6 230w panels with following specs: Voc: 36.9V Isc: 8.31A Vmp: 30.2V Imp: 7.62A What is the best panel configuration for the MPP MAX 11KW?
  12. K

    Ferrule on circuit breaker?

    Yes it has clamp style terminal. How tight should it be? Should it be impossible to take it apart with the bare hands? I tightened it the hardest I could but I can take it apart with the bare hands...
  13. K

    Ferrule on circuit breaker?

    I have some DC circuit breakers and when connecting an apropiate wire it feels loose even when tightening the screw. Is the solution to use ferrules on the wire?
  14. K

    Choosing Voltronic Axpert Max offgrid inverter

    Thanks. I'm not Italian, I'm from Norway. But maybe it's possible to have subtitles. ? Nice power arrangement you have btw. ?
  15. K

    Choosing Voltronic Axpert Max offgrid inverter

    Now I ordered Voltronic Axpert Max 8.0 from https://www.solarpower24.it The warranty time is 2 years. Is that ok? I'm excited to see how it will perform.
  16. K

    Choosing Voltronic Axpert Max offgrid inverter

    It's €70 difference on Voltronic Axpert Max 8.0 and SP24 Axpert Max 8.0 Is there any difference on the two inverters?
  17. K

    Choosing Voltronic Axpert Max offgrid inverter

    Thanks. I consider buying the 8k max1. ?
  18. K

    Choosing Voltronic Axpert Max offgrid inverter

    I'm in the process of choosing an Axpert Max offgrid inverter at https://www.solarpower24.it/category-product/inverter-en/off-grid-inverters/primo-max-en/?lang=en What is best of SP24 and Voltronic? What is best of Max1 and Max2? My impression from threads is Max1 is more tried and solid, is...
  19. K

    Using wood/plank/barge as mounting rails for solar panels on the roof.

    Is there any issues with using wood/plank/barge as mounting rails for solar panels on the roof? It's much cheaper but it's almost no one using it. Is there a reason not to use it? I found just one guy on YouTube using it:
  20. K

    Do I need isolator/solar disconnect when I have breakers?

    What is the practical difference? Isn't it completely isolated with the breakers?
  21. K

    Do I need isolator/solar disconnect when I have breakers?

    Do I need isolator/solar disconnect when I have breakers? Can I just turn off the breakers when doing maintenance on the solar panels? Like on this picture?
  22. K

    Voltronic Axpert King vs Max (I vs II?)

    What inverter did you end up with? What is your experience? ?
  23. K

    please advice pylontec 48V, voltronic axpert 4, must 5048n pv1800

    Did you upgrade to the voltronic 5000? ?
  24. K

    Inverters; Are these brands any good?

    Ok ? Why did you replace them?
  25. K

    Inverters; Are these brands any good?

    Nice. ? What Voltronic Axpert do you have?
  26. K

    OEM Voltronic and it's subsidiaries like MPP Solar

    Where did you buy from? Taiwan via ebay? ?
  27. K

    Inverters; Are these brands any good?

    What european supplier and distributor did you buy from? ?
  28. K

    DIY Solar panel mounting brackets for pitched tile roof

    I tested it on the roof. But it's a gap between the tiles: Maybe I have to trim off some of the tiles backside?
  29. K

    DIY Solar panel mounting brackets for pitched tile roof

    I try to build the brackets from angle brackets in the hardware store:
  30. K

    Zero-export inverter, not backfeed to the grid

    Ok, thanks! ? What is this local code enforcement?
  31. K

    Zero-export inverter, not backfeed to the grid

    So if I connect the grid mains to an offgrid AIO (like MPP MAX 11kw), the inverter doesn't has to be tested according to the standards (Certifications)? The inverter doesn't has to be approved and I don't have to tell the power company about it?
  32. K

    Zero-export inverter, not backfeed to the grid

    Ok great, so if I use a transfer switch the power company will consider this as "not connected to grid"? Like this? It's called semi-offgrid in this link here. Does this power transfer switch ensure it doesn't feed power back to the grid?
  33. K

    Zero-export inverter, not backfeed to the grid

    Do you mean even if I connect the mains in to an offgrid AIO, the inverter has to be tested according to one of the two standards (Certifications)? The utility gave me this answer: "As long as there is an off-grid solar system (not connected to the power grid), you do not have to send an...
  34. K

    Zero-export inverter, not backfeed to the grid

    Is these two statements contradictions? Between LydMekk and timselectric?