Search results

  1. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    So wires Wires were never crossed, turns out the inverter doesn't display readings properly and PowMr support probably knew this as their resolution to the problem was " Please use a multi meter to check your PV readings" Ended up returning it and going for a Deye 8KW Hybrid and am very happy...
  2. A

    Impossible PV Charge , what can cause this?

    Seems they are a lot more expensive in the us. I'm getting mine for around 1800USD. Maybe also cause I am getting single phase?
  3. A

    Impossible PV Charge , what can cause this?

    Depends on where you are based,I'm buying my stuff in Cebu Philippines. But attached is the data sheet
  4. A

    Impossible PV Charge , what can cause this?

    Deye 8k hybrid.. it's more expensive but seems to be more reliable as well
  5. A

    Impossible PV Charge , what can cause this?

    I ended up returning the inverter, installer came we checked all the wiring, support said if you want to check the PV Charge use a multi meter :-) so was easy decision to swap the inverter to a different brand after that
  6. A

    Impossible PV Charge , what can cause this?

    Yup i know but both led 1 and led 2 are on and I can see PV Charge kw/amp coming in.
  7. A

    Impossible PV Charge , what can cause this?

    Hey guys, So my inverter Hybrid setup is pretty messy, I now realize that the PV Solar setup might not be doing anything at all and I've been running on grid and battery for the last week. So the PowMr Hybrid inverter 5KW is displaying 4.92KW charge and 16a, however it's night outside...
  8. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    So I got a bit further in my investigation, it looks like the installers might have messed up something. Now the trick is to figure out what. I noticed that the PV Charge is always around 4.9KW even at night! That's impossible, the inverter sees it, is there a possibility that they wired the...
  9. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    Yeah i've been given a fault report document which I am going to fill in, ill do it again tomorrow first by restarting the entire system and then sending it over. If I don't connect the grid the setup is working perfectly fine but as soon as I turn on utility it switches to bypass mode directly.
  10. A

    Breaker size conflict between installer and inverter manufacturer

    I took some pictures, sorry I'm pretty much a big beginner
  11. A

    Breaker size conflict between installer and inverter manufacturer

    Thanks Guys so much. The wiring used is 25MM/4AWG. They will come tomorrow to change the breakers, hopefully that will solve the problem I'm seeing from my original post.
  12. A

    Breaker size conflict between installer and inverter manufacturer

    Hey guys, This is a follow up for a different issue I had (original post here: https://diysolarforum.com/threads/nominal-operating-voltage-360vdc-powmr-5kw-hybrid-question.40393/ ) Now the manufacturer of the hybrid inverter PowMr (5000W/80A/48v) is saying we need to use a 100A+ breaker for...
  13. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    UPDATE: Added in the additional two panels and restarted the whole system ( First Solar, Then Battery ,Then Inverter Then Utility ). This resulted in the system working and providing power directly from the panels. However after an hour or so the inverter started beeping and switched back to...
  14. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    I've messaged them but since it's Sunday I don't expect anything back yet. Getting the additional panels tomorrow installed as well to see if that sorts out the issue. Will keep you posted
  15. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    Yeah exactly, it's pretty surprising on my end as well, ill try to switch off the set for 30m and restart it to see if it makes a difference
  16. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    It's on the side of the inverter
  17. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    This is the manual, according to the listing it has a build in MPPT Solar Charge Controller
  18. A

    Nominal Operating Voltage 360VDC PowMr 5KW Hybrid question

    Hi, We have a new PowMr 5KW Hybrid inverter setup with 8x450W Panels and a 10KW / 200ah Battery. Now the system doesn't switch over to solar (Stays on bypass) and in order for it to use solar and my installer says we are lacking panels and need to add 2 panels more as the Nominal Operating...