hi everyone,
so, working on continued planning and trying to nail down wiring from my roof junction box to PV disconnect near the inverter. i'm in michigan.
NEC approved flexible MC armorlite a while ago for attic use. yay -- https://www.solaredge.com/sites/default/files//dc_pv_output_circuits_inside_building.pdf
i have a 2kw array with 8 of these 250w newpowa -- https://www.newpowa.com/products/250w-monocrystalline-solar-panel
I'm running two strings in parallel with 4 panels in series. 8 panels total. ambient temperature correction factor using 1.25 results in a theoretical....
max amps combined parallel= 27.725a
max voc= 136.4v
I'll be able to mount a wet rated junction box on a roof hip, where I'll mount a DIN rail terminal block to connect PV cable from array through conduit to 10/2 MC -- https://smile.amazon.com/Dinkle-Assembly-Jumpers-Terminal-Blocks/dp/B07TN3RLYZ/
i'll run 10/2 MC armorlite from terminal block through attic and walls down to PV DC disconnect in the basement power room.
awesome, so, 27.725 is below standard 30amp MC4 connector rating as well as 10/2 MC armorlite at all the big box stores.
but wait... what happens with attic temperature derating for the 10/2 during the summer? how do i calculate and account for that? in michigan summer we can get pretty hot, so I'm sure attic temps get up to 140degF.
so, working on continued planning and trying to nail down wiring from my roof junction box to PV disconnect near the inverter. i'm in michigan.
NEC approved flexible MC armorlite a while ago for attic use. yay -- https://www.solaredge.com/sites/default/files//dc_pv_output_circuits_inside_building.pdf
i have a 2kw array with 8 of these 250w newpowa -- https://www.newpowa.com/products/250w-monocrystalline-solar-panel
I'm running two strings in parallel with 4 panels in series. 8 panels total. ambient temperature correction factor using 1.25 results in a theoretical....
max amps combined parallel= 27.725a
max voc= 136.4v
I'll be able to mount a wet rated junction box on a roof hip, where I'll mount a DIN rail terminal block to connect PV cable from array through conduit to 10/2 MC -- https://smile.amazon.com/Dinkle-Assembly-Jumpers-Terminal-Blocks/dp/B07TN3RLYZ/
i'll run 10/2 MC armorlite from terminal block through attic and walls down to PV DC disconnect in the basement power room.
awesome, so, 27.725 is below standard 30amp MC4 connector rating as well as 10/2 MC armorlite at all the big box stores.
but wait... what happens with attic temperature derating for the 10/2 during the summer? how do i calculate and account for that? in michigan summer we can get pretty hot, so I'm sure attic temps get up to 140degF.