Hearing opposite things from two electricians whom I respect.
Background
Main panel:
125 amp busbar
100 amp overcurrent / single phase
Conductors from the Powco feed into the centerfed busbar, not lugs or breaker on top.
Inverter:
4000 Watts/50 amp OPD, so
50 amp Breaker for inverter on critical loads/subpanel
One gent says I have to derate/replace main panel/install lineside tap because the inverter breaker cannot be on the opposite end of the busbar from the main breaker.
The other gent says no problem/no need to change anything.
Trying to make sense of this....
Which is correct? (AHJ will not communicate prior to inspection.)
https://www.electricallicenserenewa...ation-Courses/NEC-Content.php?sectionID=190.0
https://www.electricallicenserenewa...ation-Courses/NEC-Content.php?sectionID=190.0
Thank you!!!
Background
Main panel:
125 amp busbar
100 amp overcurrent / single phase
Conductors from the Powco feed into the centerfed busbar, not lugs or breaker on top.
Inverter:
4000 Watts/50 amp OPD, so
50 amp Breaker for inverter on critical loads/subpanel
One gent says I have to derate/replace main panel/install lineside tap because the inverter breaker cannot be on the opposite end of the busbar from the main breaker.
The other gent says no problem/no need to change anything.
Trying to make sense of this....
Which is correct? (AHJ will not communicate prior to inspection.)
https://www.electricallicenserenewa...ation-Courses/NEC-Content.php?sectionID=190.0
https://www.electricallicenserenewa...ation-Courses/NEC-Content.php?sectionID=190.0
Thank you!!!