12000XP not compatible with 48v lead acid batteries? Unable to set absorb or equalize above 59v

ddxv

New Member
Joined
Jun 7, 2024
Messages
100
Location
Willits, California
Previously I thought the issue was just some settings, but after calling Signature Solar they told me that 59v is a hard limit set by NEC standards.

This causes an issue because the 48v lead acid battery manufacturer states the default absorb charge should be 60 and more importantly the equalize is 63v.

59v is ok for the charge, but it seems we've lost the ability to equalize our battery bank.

Does this sound correct? Is the work around to look into changing battery bank to 24v?

I get the feeling EG4 is not very compatible with lead acid batteries.
 
This causes an issue because the 48v lead acid battery manufacturer states the default absorb charge should be 60 and more importantly the equalize is 63v.

Very unusally lead-acid values. Standard is 57.6 for bulk and absorb and 54 for float. Equalize is 2.5V per cell or 60V, what batteries are you using that want such high values?
 
1000014528.jpg

Source:

Very unusally lead-acid values. Standard is 57.6 for bulk and absorb and 54 for float. Equalize is 2.5V per cell or 60V, what batteries are you using that want such high values?
Yeah? This is the manual I was looking at. Same manufacturer of our cells.
 