Allo,
I've had a 6kW setup running rather well consisting of;
Growatt 6kW and 3 Signature Solar 48V batteries. The house runs fine however I'm at or a tad over 6kW at times, wires and fuses getting fairly warm and I've had the inverter shut down now and again.
Not a big deal however I've decided to build a larger unit using Growatts 12kW unit and 4 Signature Solar batteries rather then 3.
As I crimp wires, install fuses/switches etc, I can't help but feel that this is over kill but my calcs show me otherwise.
Based on this;
12000 ac watts / .85 conversion factor / 48 volts low cutoff = 313.725490196078431 service amps
313.725490196078431 service amps / .8 fuse headroom = 392.156862745098039 fault amps
* I will only be using using roughly 7kW at times but am building the system for potential and not the moment.
Using these numbers, I went with 4/0 wire and a 48V/400A class T fuse, massive stuff compared to my 6kW setup which seems like a Tonka Toy at this point.
This time I'd like to use a DC cut off switch between the fuse and battery bank so I bought this;
Man this stuff seems yooooge, just massive but it's what I'm using.
Is this over kill?
And in terms of the DC cut off switch, would any one have a better recommendation?
I've had a 6kW setup running rather well consisting of;
Growatt 6kW and 3 Signature Solar 48V batteries. The house runs fine however I'm at or a tad over 6kW at times, wires and fuses getting fairly warm and I've had the inverter shut down now and again.
Not a big deal however I've decided to build a larger unit using Growatts 12kW unit and 4 Signature Solar batteries rather then 3.
As I crimp wires, install fuses/switches etc, I can't help but feel that this is over kill but my calcs show me otherwise.
Based on this;
12000 ac watts / .85 conversion factor / 48 volts low cutoff = 313.725490196078431 service amps
313.725490196078431 service amps / .8 fuse headroom = 392.156862745098039 fault amps
* I will only be using using roughly 7kW at times but am building the system for potential and not the moment.
Using these numbers, I went with 4/0 wire and a 48V/400A class T fuse, massive stuff compared to my 6kW setup which seems like a Tonka Toy at this point.
This time I'd like to use a DC cut off switch between the fuse and battery bank so I bought this;
Man this stuff seems yooooge, just massive but it's what I'm using.
Is this over kill?
And in terms of the DC cut off switch, would any one have a better recommendation?