Hi, need advice on a 24v System please:
My Solar array will be 1755 Watts - (with panel expansion later on)/ Total - VOC 71.1 / VMP 59.4 / IMP 29.55 in Series/Parallel (shading issues) & about a 25ft run to SCC using 4 AWG.
Solar Charge Controller (SCC) is 80 Amps /200 Volts.
Inverter is 4000W 24V.
Battery Bank(BB) - (4) 12V 300 AH Batteries in Series/Parallel (with battery balancers)- 24V 600AH Bank.
I will have (3) 15 Amp Solar fuses at each positive string and a 500V/40A DC Breaker between Solar array and SCC (4AWG) and a 500V/100A DC Breaker from SCC to Battery Bank with 4 AWG. Can anyone recommend a good brand of DC breakers? I was looking at CHTAIXI brand on Amazon but noticed they may burn up and trying to stay away from China made.
Also, on a Fuse between Batteries and Inverter, do I add a 400 AMP Class-T fuse at each positive battery terminal (4) 400AMP fuses) or 1 fuse at the main Battery Bank positive cable to the Inverter and can someone recommend a good brand as well?
I will use 2/0 and 600A busbars to connect the batteries together and 3/0 from the battery bank to Inverter - not pictured.
All in all, I probably will never exceed more than 20-30 Amps at once but looking to use good breakers and fuses.
Thanks!
My Solar array will be 1755 Watts - (with panel expansion later on)/ Total - VOC 71.1 / VMP 59.4 / IMP 29.55 in Series/Parallel (shading issues) & about a 25ft run to SCC using 4 AWG.
Solar Charge Controller (SCC) is 80 Amps /200 Volts.
Inverter is 4000W 24V.
Battery Bank(BB) - (4) 12V 300 AH Batteries in Series/Parallel (with battery balancers)- 24V 600AH Bank.
I will have (3) 15 Amp Solar fuses at each positive string and a 500V/40A DC Breaker between Solar array and SCC (4AWG) and a 500V/100A DC Breaker from SCC to Battery Bank with 4 AWG. Can anyone recommend a good brand of DC breakers? I was looking at CHTAIXI brand on Amazon but noticed they may burn up and trying to stay away from China made.
Also, on a Fuse between Batteries and Inverter, do I add a 400 AMP Class-T fuse at each positive battery terminal (4) 400AMP fuses) or 1 fuse at the main Battery Bank positive cable to the Inverter and can someone recommend a good brand as well?
I will use 2/0 and 600A busbars to connect the batteries together and 3/0 from the battery bank to Inverter - not pictured.
All in all, I probably will never exceed more than 20-30 Amps at once but looking to use good breakers and fuses.
Thanks!