Yurtle
New Member
apologies for the kindergarten level scribble scratch... hopefully legible; obviously not to physical scale
this is for a 4x4 van install
red = + side
black= - side
green = OCP
blue = devices
2 @ 280aH LiFePO4 batteries, 200A continuous (ea) BMS
2 @ 200W panels
The component accepting the two battery pos+ cables is a Bussman 1BS103 modular fuse block; so two wires in, two wires out.
Depending on stuff I haven't figured out yet I may try to use Class T rather than MRBF at the battery posts if I can figure out a good way to mount it all up.
To simplify the drawing I left out a few neg conductors and minor downstream stuff, though that is one of my questions, regarding using vehicle frame as neg current path.
Two components I'm thinking of using frame as neg are the air compressor and winch. (Not sure yet max winch amp draw but planning for a max of 400A)
Assuming correct ampacity wire and good solid connections between frame and conductors, is there a danger to other components in the system, esp vehicle computer, etc in using frame as a major current path? Also, wondering if Orion dcdc can use frame as neg?
(I was thinking I'd upgrade the engine battery ground but have realized 4/0 is overkill in that location)
I'm especially concerned after reading this post about "big kick back Voltage (back EMF)" and from Will P, "I don't think a solar specific lithium battery running a large inductive load, controlled by a semiconductor switching device is ever a good idea. It might work for a few months, but it will fail eventually. The kickback can be massive." https://diysolarforum.com/threads/how-close-can-bare-copper-bus-bars-be-12v.30555/#post-368595
Can't say I fully understand kick-back voltage and its consequences, also confused/worried about potential ground loop issues. Need further education on these topics.
Also, what is best practice for location of solar disconnect?
and, would this be an appropriate device?
MNEPV30-600-2PP
Last question... the Bussman device is "tin plated aluminum". If I put tin ferrules on the copper cables and use "no-ox-id a special" in the sockets, would that be appropriate and sufficient to prevent galvanic corrosion?

this is for a 4x4 van install
red = + side
black= - side
green = OCP
blue = devices
2 @ 280aH LiFePO4 batteries, 200A continuous (ea) BMS
2 @ 200W panels
The component accepting the two battery pos+ cables is a Bussman 1BS103 modular fuse block; so two wires in, two wires out.
Depending on stuff I haven't figured out yet I may try to use Class T rather than MRBF at the battery posts if I can figure out a good way to mount it all up.
To simplify the drawing I left out a few neg conductors and minor downstream stuff, though that is one of my questions, regarding using vehicle frame as neg current path.
Two components I'm thinking of using frame as neg are the air compressor and winch. (Not sure yet max winch amp draw but planning for a max of 400A)
Assuming correct ampacity wire and good solid connections between frame and conductors, is there a danger to other components in the system, esp vehicle computer, etc in using frame as a major current path? Also, wondering if Orion dcdc can use frame as neg?
(I was thinking I'd upgrade the engine battery ground but have realized 4/0 is overkill in that location)
I'm especially concerned after reading this post about "big kick back Voltage (back EMF)" and from Will P, "I don't think a solar specific lithium battery running a large inductive load, controlled by a semiconductor switching device is ever a good idea. It might work for a few months, but it will fail eventually. The kickback can be massive." https://diysolarforum.com/threads/how-close-can-bare-copper-bus-bars-be-12v.30555/#post-368595
Can't say I fully understand kick-back voltage and its consequences, also confused/worried about potential ground loop issues. Need further education on these topics.
Also, what is best practice for location of solar disconnect?
and, would this be an appropriate device?
MNEPV30-600-2PP
Last question... the Bussman device is "tin plated aluminum". If I put tin ferrules on the copper cables and use "no-ox-id a special" in the sockets, would that be appropriate and sufficient to prevent galvanic corrosion?