16s 280ah 48v JBD-AP20S003S wiring?

I have encountered a new problem the BMS keeps clicking immediately I turn on inverter? Please what be the cause and solution for this?
 
I have encountered a new problem the BMS keeps clicking immediately I turn on inverter? Please what be the cause and solution for this?
Screenshots of app showing cell voltages and settings please.
Did you use a precharge resistor?
 

Attachments

  • Screenshot_20240303_133123_xiaoxiang.jpg
    Screenshot_20240303_133123_xiaoxiang.jpg
    74.4 KB · Views: 3
  • Screenshot_20240303_133119_xiaoxiang.jpg
    Screenshot_20240303_133119_xiaoxiang.jpg
    85.3 KB · Views: 3
Screenshots of app showing cell voltages and settings please.
Did you use

Screenshots of app showing cell voltages and settings please.
Did you use a precharge resistor?
No I did not use a precharge resistor.
The inverter was burned due to overload issue, the electrician upon opening up the inverter showed me the burnt mosfets.
So I bought a similar inverter and connected it and then immediately I turn on the inverter the clicking sound from the bms starts.
 
Everything looks normal.
Did you use a precharge resistor?
I just replaced the bms without removing the wires from the battery, just the the harness connections and everything is looking g fine now with the new bms..
 
No I did not use a precharge resistor.
The inverter was burned due to overload issue, the electrician upon opening up the inverter showed me the burnt mosfets.
So I bought a similar inverter and connected it and then immediately I turn on the inverter the clicking sound from the bms starts.
Inrush current to charge up the capacitors could be damaging the BMS.
A precharge with a resistor is never a bad idea.
 