It's time to post some updates after the system has been in operation for 8.5 months now.
In the meantime I've finished a rebuild to change the system from using AC-in's for grid support to an "online double conversion" version, it's in "production" since January 12th now. Since this time, the house is always and exclusively driven by the off-grid inverters (no more bypass grid usage).
Many details about this rebuild are documented in the the
DIY chargenectifier thread (following my posts starting from
here).
In one of my posts I explained why I did this conversion.
The result looks like this (other pictures are in the DIY chargenectifier thread):
The main parameters are:
- 4x Huawei R4875G1 rectifiers with 75A max. charging current (4x 4kW)
- Usually they are running with 40A (~50% of max. power) to keep the fan noise low and this is enough grid support for 99% of my use cases
- placed a pair of these units on both of my battery racks
- CAN bus controlled via ESP32 controlled via ESPHome application and MQTT coupled to my smart home system (OpenHAB)
These units are extreme reliable and I like them a lot!
Some data about my solar harvest over the last 8.5 months:
Overall, my solar production declined to the lowest value in December (as expected). The forecast for January (only 6 days so far) looks like it will start to increase again in January. The grid usage value in the table for January are not longer accurate because Solar Assistant only shows grid usage via AC-in's of the AIOs which is not longer used since 01/12/2025. Instead I need to add the grid usage via the new R4875G1 rectifiers (via smart home integration).
The house load had a minimum in November because low usage of cooling and heating of the central heatpump.
The solar power over the last 90 days shows this minimum around Christmas time and started to increase at the beginning of the year.
My fan modding and the active cooling working flawless and the AIOs temperatures stay way below 50°C most of the time.
The 12 batteries are still very nice balanced between each other with low and high loads (charging and discharging), here is one example with low charging situation:
The max. cell deltas over all batteries look like this:
The average max. cell delta is between 20mV and 30mV for most of the time. A peak of about 85mV is a situation where the batteries reached 100% SOC while charging, which is ok for this (short) situation.
Here is a snapshot of the inverter view of SA for a typical situation with central heat pump running - I will say a typical load situation:
The system has no issues and the EG4-6500EX are running flawless. No dropouts no faults/errors and nearly no LED pulsing problems (sometimes a very little bit at extreme low load conditions, nearly not noticeable ).
I still think the EG4-6500EX (Axpert Max” MKS2-6500/8000) is better than its reputation. My feeling is that EG4 has sunset this inverter too early. One reason for this may be the unannounced hardware and firmware changes from Voltronic which caused a lot of problems and confusion with the EG4-6500EX about 2 years ago... who knows. For sure, the design of this Axpert Max MKS2 is really not the newest and today better options are available but it's a mature system design which usually just works after correct setup... just my 5 cents.