I got a chance to review your data and can't really make sense of some things.
There was:
* 1 point of 3min segment where only 1 battery pack was reporting.
* Inconsistent battery temp logs, it's usually reporting a fictitious number of 2 or 3 (°C) but yours went to 38,38,45,45. for 4, 3-minute segments
* and big ? issue was, for at least 8 minutes, the packs were charging at about 2.7kW level and 18kpv not reporting any of it.
This is right after you rebooted system at 10AM from previous shutdown at 7:47AM
Do you have 2 packs of the EG4 wall mounts?
Do you have another charger hooked to the batts?
You might as well post pictures of install so more eyes can vet for you.
We'd need to see settings of 18kpv to further analyze. ---> Maintenance tab, it should default to Remote Set ---> Read ---> Export PDF
Also logs of all settings changes --->Maintenance tab ---> Set Record ---> Export Data
Lastly it sounded as if you had 18 back online when speaking with EG4/SS? Any additional data logs of that?
Thanks for the attention and input. Attached is the PDF of the settings and the log from EG4/SS "troubleshooting", it was simply turning on the system with PV2, and then switching to PV3 input. No load or discharge from batteries other than to power the inverter. I could not locate the setting change log you mentioned, still learning the monitor center nuances. where is the "set record" tab?
I do have 2 eg4 indoor wall mount batteries, the 14.3 kWh packs.
I have an eg4 chargeverter attached, but it is completely isolated and is only able to energize when a generator is connected to the outside generator inlet port. I essentially added this as my grid down, no solar backup solution.
The spike you are talking about around 10 I think was just when I turned the PV input back on, it charged at 3 kw for a few seconds but then the voltage quickly bled down as shown in the video, this is the same thing that happened with PV input 3 when troubleshooting with SS, it was a much warmer day and the string size is 11 currently, so voltage was even further from Voc limits. Not sure about the inverter not reporting or where you're seeing that?
Do you know if the PV inputs are completely isolated? ie if there was damage to PV input 2, would that bleed over and damage the others?
You seem to have integrated circuit component knowledge, any ideas what component failure would lead to the PV voltage bleed like this?
I see what you're talking about, I don't know for sure, but would suspect the erratic battery readings could be related to me shutting down the system quickly as things were popping and smelling like electrical burning.