idahogal
I fixed the links, sorry!Your links don't work for me.
Panels have several ratings and they need to be known for proper setup. Voc, Vmp, Isc, and Imp.
From the panels to the battery you need a SCC (Solar charge controller). This takes the panel voltage and converts it to a proper battery charging voltage. It also has specifications for max Voc and amperage to battery.
Inverters take battery DC voltage and convert it to AC voltages. Once again it has specifications.
Between these things is wires, fuses breakers and connections. All of these must be sized based on the other components listed above.
The panel has a PWM controller with it, isn't that what is needed? I fixed the linksNo. You need a solar charge controller to connect the panel to the battery, otherwise, the panel would potentially over-charge the batteries (though their BMS should protect them) and you would definitely over-volt the inverter due to the panel's Vmp/Voc value.
Only having 110w from the panel will not adequately charge 2-100ah batteries in parallel. Even if it produces all the rated watts during a normal sunny day you are looking at about 500Wh or 45ah. It would take 5 days to reach full charge after they were discharged.
I'm only using one of the batteries. This is a very small setup, only to run a small refrigerator for now.Only having 110w from the panel will not adequately charge 2-100ah batteries in parallel. Even if it produces all the rated watts during a normal sunny day you are looking at about 500Wh or 45ah. It would take 5 days to reach full charge after they were discharged.
The linked panel kit has all that you need to connect to the batteries.
The batteries would need parallel cables and also adequate cable to the inverter. Since it is 1000w that would be covered by 4awg. A 100amp fuse would be indicated.
The inverter presently has alligator clamp things. I will need to change those out?
Ok. thanks. I can buy another controller. Any chance you'd link me to an appropriate one? Do they come with different connector types?Should be, but I'm not inclined to trust a cheap PWM controller with LFP batteries. Furthermore, PWM controllers lose out on about 20% of the available power due to the way they work, so that 110W panel will only yield around 90W peak in perfect conditions at high noon.
+1
If you only plan to use about 500Wh of energy per day, and you want 5 days worth of backup power, then this setup is fine, but once you eat into your battery backup, you'll struggle to get fully charged without reducing consumption.
I swear I don't understand why this is so confusing for me. Thank you for your help.
One like thisWhat is its consumption? Unless it's REALLY tiny, you likely don't have enough.
What fridge? Does it have a yellow energy sticker on it?
Yes. Something else to consider is that inverters consume power as well as loads.
Is this MPPT ok for my usage?Yes, change out the alligator clips for loops
You can try to run with a PWM controller but they are only about 70% efficient and they limit the panel voltage to near your battery voltage
MPPT are 95% efficient so more of your panel energy goes into the battery
I have a mini battery similar and a 1200va phoenix inverter - it will run my relatively new fridge 14 hours - an older fridge it would fail in 6 hours - in your fridge there should be a model number plate that has the specs on what it takes to run, posta pic.
ugh. I run it occasionally on my battery box (EcoFlow/Bluetti type) and it doesn't seem like it consumes that much. I just don't like to leave that battery box running 24-7. Ok, I'll deal with that later. I'd still like to charge this one battery with the 110w panel and inverter I have.![]()
320kWh of annual energy use is 320/365 = .876kWh/day
Guessing inverter uses 15W of power 24/7.
15*24 = 360Wh
.876 + .36 = 1.3kWh/day
110W of PV means you can't run this fridge/inverter.
You need at least 300W of PV, preferably 400W.
ONE battery allows for 24 hours of backup. I would use both.
400W of PV on 12V needs:
400W/14.4V = 28A of charging.
I would recommend a Victron 100/30 MPPT charge controller.
thanks for that info.It depends on usage. The standard that defines that number involves running the fridge in 90°F ambient weather while NEVER opening it. If you're running it in more mild conditions, then you won't use as much; however, the number of times its opened will increase it.
Ok, if I can just run the fridge on it at night, that would be enough.
Either way though, I would like to charge the battery with the inverter and that 110 panel I have.
haha sorry. I'd run it during the day on my battery box. Then switch to this battery overnight. I just don't like to leave the battery box on overnight, because it self-consumes so much power.Not sure what you mean. A fridge in constant operation cycles the compressor on and off as needed to maintain the internal temperature. If you choose to run it only part of the day, then it's going to run the compressor continuously to cool it down, and then start cycling it on and off as the set point is reached.
I have a notably larger fridge (10.1 cuft, but it's almost identical in consumption - probably has the same compressor). Here's what it looks like in a 24 hour period:
The blue line is the fridge cycling on and off (runs longer when it's hotter, shorter when it's cooler). The green line is my battery temperature, which is both hotter and colder than the fridge. The fridge runs about 15° cooler.
Again, if you only ran during the night, your blue line interval would be notably wider, i.e., it might run most of the night using notably more than mine for that period.
Provided you don't use more than about 0.5kWh/day, that's fine.