I have a similar capacity-loss situation with a lot of similarities to the OP. I purchased two sets of 16x 280Ah cells from Amy Wan (Luyuan) and installed them in Seplos Mason boxes with Seplos BMS. I commissioned the first set in November 2022 and the second set in March 2023.
The first set is showing a capacity loss of 15% after 2 years of operation with a total of 460 cycles. They are part of a Victron ESS system which was cycling daily from 10% to 100% SOC. Target cell voltage for 100% SOC is 3.45V.
The capacity loss was somewhat hidden initially since the SEPLOS BMS averages the SOC of the two battery packs and reports this to the Victron system on CAN. The bad pack that was losing capacity started to drop to lower than 10% while the (still) good pack would stay above 10% by the same margin, resulting in a reported SOC of 10%. It was not until the bad pack started to trigger Low SOC alarms on the BMS that I noticed the problem.
Somewhere along the way the BMS picked up that the capacity had changed and started reporting 240Ah as the "Total Capacity" (i.e. measured) rather than the rated 280Ah. The OP noticed the same thing although he had a different BMS.
I separated the two packs and after a lot of time spent top balancing the bad pack I conducted a full charge/discharge cycle shown in the attached graph. The pack was balanced within 5mV at 3.45V (Pack: 55.2V) and was discharged into normal house loads, varying a bit around 50A discharge.
The discharge knee is encountered when the SOC falls to about 15% and the battery voltage collapses below 3V before SOC falls to 12%.
The pack is recharged with 70-80A and the charge knee is encountered at about 97% SOC. My charging algorithm is designed to ensure no cell rises above 3.6V.
I don't have any cell bulging. My cell temperatures rarely rise above 30degC. I have full records on VRM.
Similarities with OP:
- Same cells;
- Same supplier;
- Same age;
- Same architecture (two parallel packs);
- Same capacity loss
I'm not convinced that using more than one SEPLOS battery with a Victron ESS system is a reliable solution without some tweaking. I'm interested to hear of others who have successfully operated such a system for 2+ years.