Why? They are at the same voltages, it's unlikely the low voltage protect level will be the same in both the BMS , so either could cut off first.The 100ah will hit zero before the 260ah ones.
Why? They are at the same voltages, it's unlikely the low voltage protect level will be the same in both the BMS , so either could cut off first.
Roughly the current share will be proportional to their capacity, 2.6 to 1, but the state of charge will be almost the same as they discharge.
Total capacity 360 Ah, if 180 amp hours is taken by the load the batteries end up at 50 Ah, 50% SOC and 130An 50% SOC.
Well I sure as heck wouldn't put BMS-based batteries in series.
Well I sure as heck wouldn't put BMS-based batteries in series.
The topic was covered here,Well I sure as heck wouldn't put BMS-based batteries in series.
AGM, GEL and sealed lead acid don't tollerate boiling.It's no problem with lead acid batteries,
Not bad, just not ideal. If you are willing to deal with the issues, go for it. You will likely have to break down the pack and fully charge/rebalance the individual batteries every few months. OR, you can use balancers between the batteries (additional expense) to keep individual batteries balanced within the pack.Batteries with separate BMS's in series is bad.