24v single cell low temp cut off

LiteSport

New Member
Joined
Aug 17, 2021
Messages
3
I have 4 Battleborn 100ah batteries that I have hooked up for a 24v system buss bar. Victron solar charger, and victron inverter.

What will happen if ONE of the internal low temp cut off trip? I am assuming that all 4 would trip at the same exact same moment. Will the single battery all the sudden see 24v at it's terminals?

Sorry if this has been asked before, I couldn't find it.
 

acdoctor

Solar Addict
Joined
Oct 5, 2020
Messages
537
Location
Central Arkansas
2S is = to 1 24 volt battery. So any interruption in that series connections and both batteries and not providing power. The other parallel battery set would be required to carry the load. If it is not capable of carrying total amps it to would be taken out. Back at the first to open bms from B- to P - would read 24 volts.
 

LiteSport

New Member
Joined
Aug 17, 2021
Messages
3
Not sure I understand, but I think you are saying that it won't hurt anything as long as the load is less then one set of batteries can put out.
 