2x Growatt SPF5000ES in parallel mode. Grid master breaker opens.
Elian
Romania
Dear all, I am looking for some kind advice I guess. I was running my hybrid system by using 1x Growatt SPF5000ES and experiencing a few overloads because load peaking above 5kwh. Otherwise no issues to report. So I got a second SPF5000ES and installed them in parallel mode. Today. All works fine as long as the inverters pull energy from the battery e.g. SBU output mode. Once I switched the Master unit to SUB (or SOL) in the evening (therefore asking to move to utility/grid), the utility master breaker (being the one of the utility provider) opens and inverters go back to battery. So I basically cannot use grid energy anymore. Is there anyone able to shed some light here please? Many thanks indeed.
Is it an RCD or regular breaker that is poping?
It is a 32A curve C breaker. Grid supplier's linked to the metering unit outside my house.
Hmm. OK. Do you have a diagram of the system?
Hope this makes any sense. Again, the 2x inverters are connected in parallel by the means of 2+2 connection cables provided by the manufacturer.
This is a picture of the breaker.
I could not find a spec sheet for that breaker but I looke up EN 61009-1 and as I suspected, it is a residual current breaker (with over-current protection).
What we don't know is if the breaker tripped due to ground current or due to overcurrent.
I am struggling to understand all the different breakers.
I am particularly confused by the breakers on the left. It looks like it is some kind of transfer switch between the grid and the inverter. Could we ge any more detail on what they are and how they are wired?
So all the 3 breakers are something like the one attached (25A btw). The one to the right (in the diagram) is for utility/grid coming in and out to inverters, both L and N. The breaker in the center is for collecting inverters output and taking it to the loads. These are meant to work together, both closed (current goes through - inverters work) or open (current does not go through, inverters are isolated). The breaker to the left is a bypass - it is always open when the other two are closed; if / when inverters are off duty (e.g. they are tripping the utility master breaker - the very case here) I can engage the breaker and the house (loads) is powered by utility directly. Hope this sheds some light.
Does the added inverter have a neutral-ground bond? That is active while grid feeds, or bonds while off-grid and doesn't open fast enough to beat the RCB tripping?
Looking at the SPF5000ES specs it seems to me that a 32A breaker is insufficient.
I agree with @FilterGuy about the diagram with all the breakers is a bit confusing.
However the spec from Growatt is hard to meet. 100A breaker on the utility inbound is not something I can accommodate nor the supplier - this is 22kwh... Meanwhile I have made a test - wired the inverters chassis together and to the grounds wire. It worked fine for like 5-10 minutes and then, while switching from an AC output mode to another (eg. SBU to SUB), the utility master breaker tripped again. So for the time being I have switched back to my initial setup (1x inverter only) and everything goes well. I really suspect my grounding is not adequate and creating the problem. The journey continues I guess.
I think I *might* understand.
Is there any type of interlock that prevents the bypass breaker from being on at the same time as the middle breaker that goes to the load? Is it possible to accidentally have them both on at the same time?
It sounds like it tripped when transitioning from grid to battery power.
I think @Hedges is on the right track. It may be due to multiple N-G bonds if both inverters have the bonding screw.
Not at this stage so technically there is such a risk / possibility. However the breakers are in separate boxes and the bypass box is locked and secured. I plan installing a switch to make things error proof.
If only the RCD decouples (32a) and no other "downstream" classic breaker (25a), is it possible that improper or missing ground to generate such an issue?
One vs. two wouldn't matter to RCB. Except, if one connects to grid while other provides line/neutral bond.
A single inverter *might* disconnect the bond with timing that doesn't cause RCB to see ground leakage. Two inverters might be timed differently.
I don't think bond in just one of two inverters would prevent this. Either switching onto or off grid, there could still be a case where one provides the bond and the other connects to grid.
If this is the issue, disabling neutral/ground bond in both inverters and connecting neutral in to neutral out could work.
Of course, any leakage to ground can trip RCB. Too many EMI filters (imbalanced between L1 and L2) can do that.
Try the switching with no loads, light loads, heavy loads. To separate RCB trip from over-current trip.
Of course, the idea that connecting to grid shorts the phases should be investigated. Try inverters connected to RCB and grid, but output Line and Neutral disconnected.
Change the host and slave inverter. You don't need to change any wiring.
It worked for me and ive expirienced the same thing.
I am curious to see what the guys can come up with here to solve it in a more technical manner.