Good question. In post 97 above I said doing so was a bad idea.What are you trying to accomplish by splitting them into two subsystems?
Good question. In post 97 above I said doing so was a bad idea.What are you trying to accomplish by splitting them into two subsystems?
Those are great suggestions for reducing/managing peak demands, but they don’t directly address whether it’s better to parallel/pool two inverters as opposed to splitting them out into two separate sub-systems.
How would one 15K pass through current > 200A ?The suggestion to reduce demand would be so two inverters aren't needed, could just use one.
I was thinking of that for while off-grid, but to provide automatic backup, would also need to limit pass-through current to less than 200A.
Or, one is separate while on-grid, but has transfer switch to be fed by inverter when grid down.
Because system already splits 400A service to 2x 200A panels, I would try having systems parallel except output. If that does work (each regulates AC voltage while supplying needed current on its branch), should avoid all issues of balancing current and switching not being exactly simultaneous.
When passing through grids to load, parallel can have issues.
I do that with 4x Sunny Island, stacked 2p2s. Each has 56A pass-through so this should support 112A on each phase of 120/240V.
I've got the pass-through current pretty well balanced, but I think at the moment of switching grid relay, it may have had excess current in one and shut down or tripped a breaker. It usually works, but I saw it trip when electric furnace and pool pump were together drawing more than 56A (no, I don't intend to run electric heat off inverter, but don't have it either automatically switched off or hard-wired to grid yet.)
Schneider doesn't even try to do that; they say to use larger external relay.
With SolArk, already has 200A internal relay. Parallel should be no problem if only for more inverter capacity, but could be a problem if pass-through current > 200A.
Ok, re-read that. I’m not investing in 400A equipment. Too expensive.Good question. In post 97 above I said doing so was a bad idea.
In the Battery Setup, you can lower the Float and Absorption voltages. Maybe drop them by 0.1 or 0.2 volts so the battery doesn't hit 100% charged.I don't think it's possible to set a charge limit of 90% and make the battery available for discharge at the same time (at least not while the grid is up). When you check the charge box on TOU I believe it locks out the ability to discharge during that time window and attempts to hold the SOC at or above the stated number.
Common Battery:Those are great suggestions for reducing/managing peak demands, but they don’t directly address whether it’s better to parallel/pool two inverters as opposed to splitting them out into two separate sub-systems.
What would happen if parallel at AC source, parallel at battery, but separate outputs?
I’m with you on that one. My very first sentence in this thread started with “If you truly need 400 amps and are planning on dual SolArk 15ks, …” I’m always skeptical of these huge systems being built, especially when they have the grid to fall back on; but I’m not well prepared to question someone else’s needs or wants when I haven’t taken any steps in their shoes. If they want 400 amps and can pay for it, so be it.The suggestion to reduce demand would be so two inverters aren't needed, could just use one.
I would need to take it out of closed-loop (SOC) mode...negating one of the best features that I spent extra money to ensure it works without drama. Besides...in closed-loop the battery stays at/under 51.7V 99.9% of the time...0.5V under the 52.2V max recommended voltage so I guess they already took your advice. Keep in mind this is a 15 cell config...hence the low(er) voltage.In the Battery Setup, you can lower the Float and Absorption voltages. Maybe drop them by 0.1 or 0.2 volts so the battery doesn't hit 100% charged.
The Skyboxes came with my head units. From what I understand HomeGrid will send you SkyBoxes for free if you didn't get them initially.@2TrevorJ I noticed in your original pics that you have the "skybox" installed on the BMS for the HomeGrid batteries. Is that from the installer while they temporarily updated firmware or does that stay inside? I ask because I dont have that inside the BMS housing and wondering if I should.
Thats great and thank you for that information. I shall request one. I did get the "Error 20" yesterday but a simple power cycle fixed it. I love the HomeGrid battery system as a whole. Just wish firmware updates were easier.The Skyboxes came with my head units. From what I understand HomeGrid will send you SkyBoxes for free if you didn't get them initially.
Supposedly you can permanently install them inside of the outer panel but I'm skeptical there's enough room. I still have yet to install those panels as I need to flip my negative battery cable connector over for clearance and I've had no reason to take the system down. I leave the skyboxes in place but unpowered since their wifi radios are always transmitting and the HomeGrid monitoring app is WAY beta.
Of note for everyone with HomeGrids - there's new firmware on the website as of the middle of last month:
I updated mine yesterday (via Skybox & USB drive) and both the head units and the individual slabs were updated. No new issues and I think it partially fixed the only (minor) issue I had where the master BMS reported 99% SOC when charged and hardly ever hit 100%. Now it's 100% about half the time. ?
My view of it is for 2 reasons I suppose:Why change the firmware? I’ve had my batteries going for 6-8 months now. Never touched them after installation.
Yea I’d just say be careful. Easy to get caught up in the gotta have the latest everything. I once did a beta firmware upgrade on my NAS. It tanked my entire NAS required hours and hours to reconstruct. After that I leave it alone and if I update it’s months after release and only official public release.My view of it is for 2 reasons I suppose:
1. To deal with the Error 20 message I got. Seems to be fixed with latest firmware. Although I dont see how I can determine my current version.
2. Potentially helping with efficiencies in battery management. Better firmware to improve battery standby loss or other code that hinders optimal operation.
Of course firmware can break things too.
Transformers have multiple taps. You should call and ask them to check; adjusting it isn't that hard. Damage from over-voltage is long-term degradation, so you do not see the effects right away.I haven't posted in here in a bit because outside of troubleshooting my Emporia EVSE charger's "excess solar" function the system has been working perfectly. Zero drama/issues/hiccups/weirdness.
Trying to decide if I want to reach out to the utility. I mean...their engineering fully approved my setup but I still don't want to stir the pot and have them potentially ask me to limit my export (booooo!). Is there anything they can do with the transformer (other than replace it)? One variable is there are still 6 or 7 houses on my street that are vacant; brand new and unsold. Local load is sure to increase once they're occupied.
Looks like there are six 50 kVa 14.4 kV transformers on my street feeding roughly 30 single family houses. So...maybe 5 houses?How many homes are fed by the one transformet?
It depends on if the distribution circuit is over-voltage or just the local transformer. The distribution transformers often have automatic tap changers which work in smaller increments.I did some reading and looks like those taps are usually 2.5% increments. Does that mean they could potentially drop the voltage to ~243v?