Just built a (see post title) 1000ah LiFePo4 battery for my Ford Transit van build. I am using the 500A Daly BMS.
I have a 450W solar set up with MPPT charging along with my DC-DC which I've yet to install.
Question: I would like to set up shore power charging. I'm a noob watching only YouTube videos. Any recommendations on an AC-DC charger? Thx in advance.

(picture is my temporary set up. It'll get cleaned up)

IMG_20211013_165823.jpg
 

kenryan

Solar Addict
Joined
Jun 29, 2021
Messages
154
I have had good luck with Magnum Inverter/chargers. Note: you need to get the remote to change and set charge parameters.
 

jomac915

New Member
Joined
Oct 22, 2021
Messages
7
I already have a 5000W GIANDEL pure sine inverter. I guess I was thinking I need a separate AC to DC charger. The Victron IP65. Thoughts?
 

rmaddy

Full-time Solar-powered Trailer Life
Joined
Nov 16, 2019
Messages
1,742
Location
USA
5000W inverter on a 12V system? How do you plan to wire that? You really should be looking at a 48V battery to use a 5000W inverter.
 

smoothJoey

Hoop Dee Doo!
Joined
Nov 30, 2019
Messages
10,012
5000 ac watts / .85 conversion factor / 12 volts low cutoff = 490.196078431 service amps
490.196078431 service amps / .8 fuse headroom = 612.745098039 fault amps
 

jomac915

New Member
Joined
Oct 22, 2021
Messages
7
5000W inverter on a 12V system? How do you plan to wire that? You really should be looking at a 48V battery to use a 5000W inverter.
Just thought about going with the biggest. I'm running an AC fridge and she wants her 1600W induction cooktop and our 1000W microwave.
 

rmaddy

Full-time Solar-powered Trailer Life
Joined
Nov 16, 2019
Messages
1,742
Location
USA
Those numbers make my point. For a 5000W inverter and a 12V battery you need wiring that can handle 500A. That’s massive and dangerous. You would need dual 4/0 cables per connection. That’s difficult and expensive. And can the inverter even support such a connection?
 

smoothJoey

Hoop Dee Doo!
Joined
Nov 30, 2019
Messages
10,012
Joey can you explain this in layman's term?
Service amps is the maximum draw of the inverter in normal operation.
To avoid nuisance trips we / .8 to add a bit of headroom for the fuse which gives fault amps.
The wire has to be rated for at least fault amps so that the fuse blows before the insulation on the wire melts or burns.
The largest widely available wire suitable for our application is 4/0 awg welding cable.
4/0 awg pure copper wire with insulation rated for 105C is good for ~400 amps.
After 4/0 awg you either have to double the cables or start using cable that is measured in circular mills.
I agree with @rmaddy 2x 4/0 awg is required.
Alternatively 1x 400MCM.
 

jomac915

New Member
Joined
Oct 22, 2021
Messages
7
Those numbers make my point. For a 5000W inverter and a 12V battery you need wiring that can handle 500A. That’s massive and dangerous. You would need dual 4/0 cables per connection. That’s difficult and expensive. And can the inverter even support such a connection?
Yes, currently the inverter is set up for dual 4/0 cable. It came that way.
 

jomac915

New Member
Joined
Oct 22, 2021
Messages
7
Service amps is the maximum draw of the inverter in normal operation.
To avoid nuisance trips we / .8 to add a bit of headroom for the fuse which gives fault amps.
The wire has to be rated for at least fault amps so that the fuse blows before the insulation on the wire melts or burns.
The largest widely available wire suitable for our application is 4/0 awg welding cable.
4/0 awg pure copper wire with insulation rated for 105C is good for ~400 amps.
After 4/0 awg you either have to double the cables or start using cable that is measured in circular mills.
I agree with @rmaddy 2x 4/0 awg is required.
Alternatively 1x 400MCM.
I have access to both. 400MCM and 4/0 with the higher rated insulation.
 