I got this bolt on terminal fuse block that has a 5/16 fuse holder bolt where the cable attaches. My cable has 3/8 lugs. Is is okay to use the 3/8 lug (it is snug when bolted down) or should I redo the cable with 5/16 lug?
To me it is all about surface area contact for the Amps traveling through the connection. I don't have a picture of your particular connection so I can't say for sure. If it is like my Bussman fuses there is not inside contact surface between the 3/8" diameter of the fuse surface and the 5/16 bolt so in that case I would just make sure the lug contacts all of the fuse contact area.......My cable has 3/8 lugs. Is is okay to use the 3/8 lug (it is snug when bolted down) or should I redo the cable with 5/16 lug?
That looks like a ring terminal probably 8 awg or less, confirm?
Use a 15 amp fuse and don't worry about the size mismatch because the ampacity is small.12 AWG, for my Renogy Wanderer 10A SCC to battery. The fuse is for my 2 AWG inverter to battery cable, too lazy to grab it from the garage for the photo.
The SCC also needs a 10A fuse to the battery according to Renogy. Is that correct?
Use a 15 amp fuse and don't worry about the size mismatch because the ampacity is small.
That could carry 100 Amps so it depends on the fuse or what you expect the circuit needs to carry.
AtcThanks, will do. That’ll have to be ANL/inline?
As long as that is the correct fuse for that wire size you should be okay if you make sure the fuse surface contacts the lug all the way around.
The fuse is to protect the wire. The fuse and wire should be sized to handle the Inverter load, which in your case the wire will easily handle the load. On a short circuit the fuse will blow quickly. If the inverter surges above 100 Amps the wire can handle it for a while before getting too hot and your fuse won't blow. I am more specific and conservative with wires in my home inside conduit but wire in the open air can tolerate more heat and Amperage. You will probably get several opinions.Should the fuse be based on my 1200W inverter or my 2 AWG cable?
10.5 | Low voltage cutoff |
2000 | Inverter rating |
190.4762 | Expected Amps |
285.7143 | Expected Amps * 1.5 |
342.8571 | Fuse rating |
12 | Battery rated voltage | |
2000 | Inverter rating | |
166.6667 | Expected Amps | |
250 | Expected Amps * 1.5 | |
300 | Fuse ratin is Expected safety margin in amps *1.2 |
14.8 | Battery charging voltage |
2000 | Inverter rating |
135.1351 | Expected Amps |
202.7027 | Expected Amps * 1.5 |
243.2432 | Fuse ratin is Expected safety margin in amps *1.2 |