I have done a complete video teardown on these breakers in the past.
* They have both Thermal and Magnetic Trip
* They have ark arrestors for DC
Model Number:
TXC65Z-60
B32
Amazon Links:
Double Pole Purchase Link
Single Pole Purchase Link
The Magnetic trip is actually quite sensitive and triggers very easy on transients. The Thermal Breaker is NON OPERATIONAL and will pass 90ADC continuous.

I also have a bunch of the 1000V rated Genuine... (-63) and those actually work.
These in green are hazardous waste. If you have them in your system, I strongly urge you to perform an overcurrent test IMMEDIATELY. They will protect you from a short circuit and they will allow you to turn loads on and off... BUT THEY ARE NOT 32A BREAKERS. THEY ARE 32A PASSERS.
* You wont find them on MFG website
* You wont find a legit datasheet anywhere on the Webberz
Todays Vblog showing that I can run 90A continuous thru these breakers until my SB50's melt down. Total Hazmat.

I was running various 90C - 105C 10AWG on these breakers and yesterday I saw 45A pass... then today I ran 60A... then 90A... then S M O K E S H O W as expected. Super glad I performed the test and found the safety devices dont work. Especially while running lower temperature SB50's.
Good Luck in your Venture
Test but Verify