Original system(May 2024) 2 EG4 6000XP with 10KW PV that were feeding 100amp main panel and they would hit 100% output and went into overload couple times. Since the original plan was to go with 3 I Added #3 inverter(two weeks ago). All the panels were switched out to larger system currently ~15KW producing up to 70KWh(yesterdays record for winter). 5 strings total: inverter #1 (2 strings); inverter #2 (2 strings); inverter #3(new one) 1 string. All three inverters are connected to 2 PowerPro 14.3KWh batteries+1 DIY kit 15KWh + 1 EG4 LL for a total of 50KWh. I was producing too much power so I mixed the batteries a bit. Switching out to 150KWh batteries withing two weeks, selling/reusing these in other setups. Also a Chargeverter is wired in or the backup, works wonderful with 120V 28A cheap genny.



Everything runs the house fine, charges the batteries without problems, discharges fine. App controls work fine besides the app crashing.
All inverters are wired in parallel feeding a 100amp subpanel. All AC 240 inputs and outputs are identical 6gauge THHN through 40A Breakers.
Now the funny, not so funny part. #1(master) and #2 will output about the same amount of power while the #3 will always be about 50% of the other two.
#1 inverter 60% load
#2 inverter 57% load
#3 inverter 30% load
Its always consistent. #3 is always 1/2 of what the #1 or #2 is showing as output. If I kill #1 or #2 separately, #3 is still at 50% of the #1 or #2 is putting out according to %. Even when sun is down and pulling from battery only.
Restarting, multiple times and cycling EPS output doesn't help. Any ideas please.
Again all outputs and inputs are in separate combiner panels. #1and#2 will ramp up together, #3 lags behind running @50% capacity of either 1 or 2
All battery cables are New EG4 PowerPro paralleling cables. All same connectors. It's consistent disrepancy between them. HELP please



Everything runs the house fine, charges the batteries without problems, discharges fine. App controls work fine besides the app crashing.
All inverters are wired in parallel feeding a 100amp subpanel. All AC 240 inputs and outputs are identical 6gauge THHN through 40A Breakers.
Now the funny, not so funny part. #1(master) and #2 will output about the same amount of power while the #3 will always be about 50% of the other two.
#1 inverter 60% load
#2 inverter 57% load
#3 inverter 30% load
Its always consistent. #3 is always 1/2 of what the #1 or #2 is showing as output. If I kill #1 or #2 separately, #3 is still at 50% of the #1 or #2 is putting out according to %. Even when sun is down and pulling from battery only.
Restarting, multiple times and cycling EPS output doesn't help. Any ideas please.
Again all outputs and inputs are in separate combiner panels. #1and#2 will ramp up together, #3 lags behind running @50% capacity of either 1 or 2
All battery cables are New EG4 PowerPro paralleling cables. All same connectors. It's consistent disrepancy between them. HELP please