4/0 cable: Pushing Over the Current Limit

So here is a question - do you really want a 221f wire around? Meaning if you intend running wires hot you have to take into account what it is touching. You could melt plastic or soften it if it is a shelf support that could be trouble.
No, that’s why I run all 20/0 wire.
 
Last edited:
Keep in mind with 3 6000xps you'll be be running them at absolute max charger capability of 140 amps each. I wouldn't do it.
 
I personally am not comfortable running anything much past 140f unless im REALLY unlikely to touch it. No way in hell do i want a 100c anything anywhere where i can touch it, at least as a design choice...

Which is funny.. because im an auto tech and there are nuuuuumerous spaces way over that on a running or recently running engine bay, and i work around that just fine. But other than getting my hand sucked into a running belt drive or bounced off a spinning fan, burns are the ONLY concern im really worried about there. It's kind of like how i explain shock danger to my students: A housecat is not that dangerous, but it might be if you are already on a ladder. I dont want to experience any reflexive jerking movements in an environment where something ELSE is even more dangerous. I can touch 140f+ without 'jerking' away from it, but 100c probably not! And then bam, jam the other end of the same arm into some 200-400v something or other terminals and make it worse? Yeah, should try and protect those from incidental contact too etc etc but if im in 'reflex mode' there's not much that is totally stupid proof..

Maybe im paranoid but that's how i think about safety. I dont want anything painful enough to induce reflexive movement into something even more painful. :ROFLMAO:
 
Math time...

400A through 20' of 4/0 is seeing 1mΩ of resistance and generating 157W of heat. That's 2.5X 60W incandescent bulbs being pumped into 13# of copper that has 20 linear feet worth of surface area from which it's dissipating that heat.

Can we all put our vajeens away now?

I'm voting for NEC open air rating of 405A or 28A per battery. Pretty close to target.

If you have an IR gun handy, check temps, so you know you're under 105°C, especially at the lugs/crimps.


How hard can I push the 4/0 ??. I want to get up to 30A/battery but that would be 30x14=420A (probably too much).

No need to wait for a heat gun to tell you where/if there's a problem. Just need to check the Voltage drop.

To me the easy math and super quick test is V x A = Watts = Heat

Also in my experience it's not the wire that's going to get you, it's the connections and usually it's the breakers. Also, from what I've seen breakers have more resistance than an equivalent fuse.

I carefully run every new system up to it's full rating while checking voltage drop across the entire system as well as every terminal, fuse and breaker.

EG: 1V drop across the entire 48v system @ 420 amps = 420 watts of heat.

Most important is finding what is responsible for that 1V. EG: 50% of it one connection or it's evenly spread out across the whole system?

Try it sometime, it's very informative.
 
That's for 105°C rated UL 1426/Marine wire.

Please confirm your insulation rating before you go crazy with things... :)
Exactly, please check insulation temp rating everyone.

Many here would be incredibly surprised at how much current these cables can actually handle.

I don't want to come off as a bad example but I've been able to push a ridiculous amount of current through small conductors 😂 200c rating silicone wire is supreme.
 
Something else to mention is even if your conductor and insulation and lug can handle the temperature, the terminal you are connecting to might not. Especially if it's a breaker.

These devices have temperature ratings and you cannot ignore them! Just because your wire can handle it doesn't mean everything else can.
 
I personally am not comfortable running anything much past 140f unless im REALLY unlikely to touch it. No way in hell do i want a 100c anything anywhere where i can touch it, at least as a design choice...

Which is funny.. because im an auto tech and there are nuuuuumerous spaces way over that on a running or recently running engine bay, and i work around that just fine. But other than getting my hand sucked into a running belt drive or bounced off a spinning fan, burns are the ONLY concern im really worried about there. It's kind of like how i explain shock danger to my students: A housecat is not that dangerous, but it might be if you are already on a ladder. I dont want to experience any reflexive jerking movements in an environment where something ELSE is even more dangerous. I can touch 140f+ without 'jerking' away from it, but 100c probably not! And then bam, jam the other end of the same arm into some 200-400v something or other terminals and make it worse? Yeah, should try and protect those from incidental contact too etc etc but if im in 'reflex mode' there's not much that is totally stupid proof..

Maybe im paranoid but that's how i think about safety. I dont want anything painful enough to induce reflexive movement into something even more painful. :ROFLMAO:
I just imagined a cascading event of you touching one thing hot, jerking back "OW" and smacking something live, sparks fly "YOW!!" Ricochet off that and bounce off the hot thing back to the high voltage and more sparks and sizzles back and forth cartoon style
 
No need to wait for a heat gun to tell you where/if there's a problem. Just need to check the Voltage drop.

To me the easy math and super quick test is V x A = Watts = Heat

Also in my experience it's not the wire that's going to get you, it's the connections and usually it's the breakers. Also, from what I've seen breakers have more resistance than an equivalent fuse.

I carefully run every new system up to it's full rating while checking voltage drop across the entire system as well as every terminal, fuse and breaker.

EG: 1V drop across the entire 48v system @ 420 amps = 420 watts of heat.

Most important is finding what is responsible for that 1V. EG: 50% of it one connection or it's evenly spread out across the whole system?

Try it sometime, it's very informative.
Excellent advise. Now I just need to wait for a sunny day to test it. Cloud city in NE Ohio today.
 
I just imagined a cascading event of you touching one thing hot, jerking back "OW" and smacking something live, sparks fly "YOW!!" Ricochet off that and bounce off the hot thing back to the high voltage and more sparks and sizzles back and forth cartoon style
Exactly! Murphy's Law dictates my dumb ass will suffer the most outrageous perfect storm of bullshit, so i try to keep that in mind when thinking of 'small' dangers.. they could lead to bigger ones!
 
I was working to fix similar issue by using 2nd pair of 4/0 cables and a 2nd 250A breaker. The key to doing that is being able to get a mechanical interlock between the two breakers so that if one trips they both trip. The two 250A breakers were much cheaper then upgrading to a much larger breaker and subsequent larger cables.
 
I was working to fix similar issue by using 2nd pair of 4/0 cables and a 2nd 250A breaker. The key to doing that is being able to get a mechanical interlock between the two breakers so that if one trips they both trip. The two 250A breakers were much cheaper then upgrading to a much larger breaker and subsequent larger cables.

How did you solve it? a bar across all 4 handles? a 4 pole breaker? something else?
 
Math time...

400A through 20' of 4/0 is seeing 1mΩ of resistance and generating 157W of heat. That's 2.5X 60W incandescent bulbs being pumped into 13# of copper that has 20 linear feet worth of surface area from which it's dissipating that heat.

Can we all put our vajeens away now?

I'm voting for NEC open air rating of 405A or 28A per battery. Pretty close to target.

If you have an IR gun handy, check temps, so you know you're under 105°C, especially at the lugs/crimps.

Don’t ever change. 🍻
 
Math time...

400A through 20' of 4/0 is seeing 1mΩ of resistance and generating 157W of heat. That's 2.5X 60W incandescent bulbs being pumped into 13# of copper that has 20 linear feet worth of surface area (346 sq-in) from which it's dissipating that heat.

Can we all put our vajeens away now?

I'm voting for NEC open air rating of 405A or 28A per battery. Pretty close to target.

If you have an IR gun handy, check temps, so you know you're under 105°C, especially at the lugs/crimps.
I will only do this in the crappy seasons for solar in NE Ohio (Dec Jan Feb) to capitalize when the sun pops out for a short time. In the other months I keep the charge current about 230A (for 14 batteries). On the plus side the 157W in winter helps with heating a little.
 
Checked it: 600V, 105degC welding cable. Happy I don't have to spend more $$$ this solar is getting expensive :eek:
Going to be HOT!!!!

300mcm 90c 400 amps free air ( times three on a 1200 amp breaker )
But it’s hot
At full load your not going to touch one of those phases feeding the main
You will burn your hand

I never ran super flex at temperatures higher than I would 90c pvc or nylon just because that so much heat it’s bad fur everything around it

IMG_7533.jpeg
 
Last edited:
Going to be HOT!!!!

300mcm 90c 400 amps free air ( times three on a 1200 amp breaker )
But it’s hot
At full load your not going to touch one of those phases feeding the main
You will burn your hand

I never ran super flex at temperatures higher than I would 90c pvc or nylon just because that so much heat it’s bad fur everything around it

View attachment 260445
Sunshine_eggo said it's only 157w over 20ft., doesn't seem too bad for a few hrs when we have full sun. Not going to grill any hotdogs with it :ROFLMAO:
 
Sunshine_eggo said it's only 157w over 20ft., doesn't seem too bad for a few hrs when we have full sun. Not going to grill any hotdogs with it :ROFLMAO:
Heat has to go someplace...

9 watt LED.
1733270162431.jpeg
Put it in a closed or semi closed light fixture and it could set you house on fire, but its only 9 watts...
Old fixture may have been rated for 100 watts of incandescent but they never caught fire.
Its what else might be cooked with the device in that localized heat you need to consider
 