Fuses has multiple purposes.
- Protect your cable (less A than cable allowed)
- protect your battery (less A than battery can charge/discharge)
- protect your equipment (less A than equipment can max use/make)
- ....
For example you have a 4p battery system, and some inverters (bigger system)
Where do you put and what size fuses ?
- Fuse 1 to 4 sized based on battery. 280Ah battery should not charge/discharge over 1C: 300A
- Even with 3 battery strings out of order the inverters will work and can use up to 300A from remaining 1 battery. Also they can not overuse it.
- Fuse 0 based on inverters. Like 3x 8kW inverter can use 500A (x1,5 peak): 700A
And now for the questions:
- Why do I need a fuse on both leg?
Because a short can occur in the unprotected leg. And that gets around your only fuse and that is like you did not have it at all.
- Why disconnect both leg?
To completely remove the battery from the circuit. To make it easy to service.
- Why an extra fuse before the inverters?
Because F1+F2+F3+F4 together will allow too much: 1200A (and not 700A).
- Why bother with that lot of fuses? I am handy, never dropped a tool. I am certain I will not make a short!
Good boy But you know sometimes accidents happen. Sometimes years later. Sometimes outside forces you can not control.
These are the principles how I design the fuses on a bigger system.
Some will say overkill. I will say safety and foresight.