LotsOPower
New Member
Planning out a system for my house that has 400A service. There is a meter/main panel outside with a 320A meter and 400A main breaker, which uses parallel conductors to feed an Eaton IFS in the basement. Those parallel conductors land in a 400A breaker, which then feeds four 200A and one 400A sub-panel, each with their own 200A/400A breaker...
The short version is that I can't bring myself to completely rewire the IFS, so I had been planning to parallel two Sol-Ark 15K inverters, where each has the 200A pass-through, and some amount of PV+batteries that isn't super important to this thread. With the recent Sol-Ark/Deye fun, I started looking at EG4, but ran into a few questions after EG4 published an "EG4 400 Amp Residential Service System Wiring Diagrams" guide in December, but all 3 diagrams say: "This wiring diagram applies to a “400 Amp residential” service (400 Amp nominal Residential Service Entrances are really rated to 320 Amps split into 2 200 Amp Services. It does not apply to a True 400 Amp service with a single 400 Amp Main Breaker."
The short version is that I can't bring myself to completely rewire the IFS, so I had been planning to parallel two Sol-Ark 15K inverters, where each has the 200A pass-through, and some amount of PV+batteries that isn't super important to this thread. With the recent Sol-Ark/Deye fun, I started looking at EG4, but ran into a few questions after EG4 published an "EG4 400 Amp Residential Service System Wiring Diagrams" guide in December, but all 3 diagrams say: "This wiring diagram applies to a “400 Amp residential” service (400 Amp nominal Residential Service Entrances are really rated to 320 Amps split into 2 200 Amp Services. It does not apply to a True 400 Amp service with a single 400 Amp Main Breaker."
- Does this actually require the meter/main to have two separate 200A breakers instead of parallel conductors coming off a 400A breaker?
- Does the Sol-Ark require the same and I just hadn't seen it?
- ... I suppose this makes sense given the Churod 200A relays used in the pass-through (55A make/break spec???) need limited to 200A, and under normal conditions that would be the case, but if one of the parallel inverters dies and the relay stays open, the other parallel conductor feeding inverter#2 with a closed relay could see the full load, but I'd expect inverters that are parallel capable to communicate with each-other and prevent this scenario.
- EG4 diagrams with GridBOSS do not show the parallel 200A circuits recombining to a 400A panel
- Appears to be supported in the 18kPV with NO GridBOSS (diagram #3) ... well, kind of (via 70A back fed breakers)
- Sol-Ark shows this in their 15k parallel diagrams, and I've seen it in several YouTube install videos as well)...