Hey folks, wanted to share my setup and talk ground mount solar. Having done a roof setup at my last house, I am a huge proponent of ground mount if space allows. Happy to answer questions, and certainly a lot of my lessons learned are my opinions rather than hard fact.
A little bit about me...I am 100% DIY and self taught. Gained experience over the years with a lot of renos and hobby/DIY work. Work in tech and have done some embedded hardware work as well as commercial data center work that provided a bit of a foundation I guess
System components:
Design considerations
A little bit about me...I am 100% DIY and self taught. Gained experience over the years with a lot of renos and hobby/DIY work. Work in tech and have done some embedded hardware work as well as commercial data center work that provided a bit of a foundation I guess

System components:
- 2x Sol-Ark 15K in parallel, zero-export to grid AKA sell-to-home setup.
- 12x Orient Power 48V230 LFP batteries
- Wired in parallel in 4 groups of 3 with a class T fuse for each group
- 2x ground mount arrays, 23kW each
- 48x Q Cells Q.PEAK DUO XL-G10.C 480W per array
- 6 strings of 8 panels per array, strings paralleled in groups of 2 to feed 3 MPPTs per Sol-ark
- DC disconnects with DC surge protectors at each array
- IronRidge racking. XR100 rails and associated components, no optional diagonal bracing.
- Roughly 46kW PV, 35kW AC output, and 144kWh battery storage in total.
- Maximum generation is approximately 300kWh a day +/- 15%.
Design considerations
- Ground mount at a shallow angle as to not exceed the fence height and be an eyesore
- Absolutely 0 power equipment / inverters mounted outside. I think people in AZ are crazy for mounting inverters and load centers outside. Service disconnects are OK but nothing else IMHO.
- All power equipment/inverters/batteries grouped together in one side of the guest house garage.
- Guest house powered 100% off of inverter load outputs. Zero-export back to the main house. Full load/backup of the main house is not practical due to split 400A service with load centers on both sides of the house and space/distance/cost constraints.
- Having the PV/batteries act as a UPS for the networking/IT equipment co-located in the guest house is also critical, as the property has an extensive on-site video surveillance system.
- 100% off-grid / zero-export consumption offset sizing on typical full sun days
- Property consumes roughly 275-300kWh a day with pool equipment, ACs/heat pumps, and 2 EVs.
- Some minor grid usage (10-20kW) in April/May and October/November due to the 12kW pool heat pump running which is an absolute pig on power.
- No modification of existing service entrance or electrical at the main house for permitting complexity reasons.
- Fully permitted PV/inverters during construction time. Battery expansion at a later date.
- No flammable materials used for any battery racking and no battery wiring run inside walls. Everything in open-air or metal raceways or metal racking.
- Always run a bigger conduit than you need, makes wire pulls much easier. 20% fill on a 2" SCH40 PVC....totally fine right? Do 2.5" anyway.
- Insulated multi-tap connectors are your best friend. Polaris, Burndy, Panduit...
- A ditch witch that can go at least 24” deep is worth the rental money. Digging more than a few ft by hand for conduit in AZ clay soil is brutal work.
- Splitting AC and DC in a wire trough / raceway is a colossal PITA. I'm fortunate I was inspected under the 2013 code and didn't have to deal with it. I don't envy folks who have to deal with it.
- Always oversize conductors or run extra conductors for possible future expansion.
- If you care about the longevity of inverters and breakers and batteries, don't put them outside in dusty or hot climates despite conventional or local wisdom. Fight the inspectors and put it indoors. The NEC allows it.
- Ground screws are awesome. I did the first array with 3" mechanical pipe floated in 14 (2x7) 24" holes filled with concrete, and the second array with 2" mechanical pipe, 22 (11x2) 4ft long ground screw piers. Absolutely would use ground screws again for everything. Hiring a concrete pump and renting a skid steer to auger 2' wide holes SUCKS and adds up to more $$$ at the end of the day, not to mention the landscaping disruptions.
- U.S Wholesale pipe is the only DIY-friendly mechanical pipe supplier I've come across.
- The price premium for IronRidge racking is worth it for the design and layout tools, engineered plans, GreenLancer permit drawing services, availability of materials, etc.
- Zero-export with CTs is a necessary evil for me but adds a lot of complexity and failure points. If you are doing brand new construction...have a 3-way disconnect for service/grid/inverter switch and use the 200A passthrough of the Sol-ark.
- If you're doing Zero-Export, crank up the zero-export target from 20W to like 100W per inverter. With a very large system like this, the inverters just don't do 20W properly and inadvertently export too much, possibly getting you in trouble with the utility. You won't be truly 100% grid offset...maybe 4-5kWh of grid usage a day, but the system will operate much more smoothly.
- Nailed the panel to inverter ratio. 35kW AC capacity from the inverters at 100% load, 46kW solar....A little bit of clipping from 10AM-2PM but confident it's the right balance for long term longevity of the system and aligned very nicely with buying panels by the pallet for cost reasons. Have about 6kW of panels left over in the garage for future replacement/hail damage if it happens.
- A high quality shielded 18/4 wire from Belden is suitable for for extending CT wires by 100ft for Zero-Export. I was worried about zero-export when the inverters aren't right beside the service entrance, but it works fine.
- Did 2" mechanical pipe for one array and 3" mechanical pipe for the other. Thought minimizing holes in the ground was the priority and 3" was easier. WRONG. 2" pipe is way lighter and easier to work with and cut, by a huge margin. Make the extra holes!
- The NEC, utility regulations, inspections, permitting, etc. are one big expensive bureaucratic mess that disincentives DIY work and provides little/no safety or value, and treads on individual rights and freedoms. I "played ball" this time but haven't in the past, and gained absolutely nothing for it. I failed one inspection throughout the whole process for using a sticker instead of a riveted placard for the voltage/amps on the AC disconnect.
- I should really put some white gravel down to benefit from bifacial gain. I got a good deal on the panels but didn't strictly need bifacial ones...I just wanted the utility/XL sized panels and these were good value.
- I like the Sol-Ark hardware, but not the software. I know they're getting better, but the security aspect of their data loggers and remote firmware updates is scary. I recommend doing a 1-time update, then yanking all of that stuff and running Solar-Assistant.
- I've done the DIY battery pack from raw cells before at my last house, and I had many many regrets. The server rack batteries are a clear winner IMHO, as long as the BMS boards stand the test of time... Only other product I’d use at this scale is Tesla Powerwall because the integration and software is lightyears ahead of the DIY solar market, but they have to figure out the cost and the DIY-Installer hatred before I jump in.
- Chain-link fence/cage around the interior solar equipment and batteries for child safety.
- Test Sol-ark GEN input with the Cybertruck