Not yet. I'll think about it for a couple of days.
The BMS will cut the discharge path at 150A. The fuse will work at 150A for several minutes (if we accept that it was a genuine fuse). To be above 150A the only option seems to be a short circuit. And a short circuit would leave some marks. If it was the inverter, then it would not be working fine after that.
I'll look at the old logs to confirm that this is an exceptional case. I'll look also at the documentation for details on the event. Since this was like 5 minutes before the fuse failure I have some doubts that it is related. The event timestamps between the two systems have always been 1:1 till now, so I'm considering them correct. And I see no issues reported from the BMS (like spikes).
The BMS will cut the discharge path at 150A. The fuse will work at 150A for several minutes (if we accept that it was a genuine fuse). To be above 150A the only option seems to be a short circuit. And a short circuit would leave some marks. If it was the inverter, then it would not be working fine after that.
I'll look at the old logs to confirm that this is an exceptional case. I'll look also at the documentation for details on the event. Since this was like 5 minutes before the fuse failure I have some doubts that it is related. The event timestamps between the two systems have always been 1:1 till now, so I'm considering them correct. And I see no issues reported from the BMS (like spikes).