BinaryMaestro
New Member
Hello! Long time lurker, first time poster.
I am building out a power system for our 46' 5th wheel as we begin our fulltime RV living.
We plan on being nomad's for several years staying mostly in boondocking sites. We work remotely and have dogs so we need to be able to run A/C's (if needed) and power our workstations, monitors, network, etc.
We have 3 standard RV dometic penguin II A/Cs (2 with heatpump). I know that I can't plan to run all 3 all day, but would like the system sized large enough that I could run all 3 plus the microwave, tv, fridge, computer if I wanted (even for just 1 hour). I can run the generator if I need to run them a lot. Ideally we would not be parked in a heat dome, but.. that might be hard to do sometimes.
This has led me down the ~10kva/10kw 48v inverter path. *I have not performed a power audit yet as we are still living / working in our house, it's currently 100+ degrees and we have no grid connection at the RV's location (family members land).
I would like to have 25-30kwh of power stored via ecoworthy server rack batteries in the storage passthrough. We are towing with a converted Semi Tractor "toterhome" so pinweight isn't a big issue. I will put as many solar panels on the roof as I can fit. I have not determined what panels due to required VOC for MPPT. Currently have 2 sets of wires running from roof to passthrough. Potentially adding an additional ground array (after real world testing) if needed.
As the weather starts cooling down I plan to begin installing the system so that I can move into the RV and work on completing the install (inevitably troubleshooting it) and breaking it in.
Since we're currently stationary, I can lay the panels on the ground for now to obtain power as well as running the generator when additional power/charging is needed. Then work on roof mount (unistrut) as time and weather permit.
At this point I've spent 100+ hours researching components and other builds. I've spoken with a couple professional RV solar installers (one who said 12v only for RVs, one said 48v only for this size). I'm not at all concerned about having 12v 48v and 120v systems in my RV. I'm not an electrician but work in the technology industry and have had many hobbies that use various battery types and voltages.
I've been looking at using Ecoworthy and SRNE components due to their cost, reputation, and receiving a random guy on the internet named Will's blessing. *Thanks for everything you do Will!*
I am now asking for your thoughts on the potential systems that I am considering and if anyone has any experience with the non-Victron components. Am I totally missing something?
Thanks for taking the time to read this and for providing any input.
46 ft 5th wheel
50amp 120v (no 240v appliances)
Onan 5500 Genset Single Phase 2x 30a breaker
System comparison
Batteries - Looking at 5-6x Ecoworthy V3 Server Rack 48v 100ah to be able to utilize comms.
2x Victron Quattro 5k - I know this has been done in many RV's and hits all my requirements. However, it's expensive, heavy, and large. Much more complex. Can still run 1 leg if an inverter fails. PV Charging/Inverter can fail separately. Min VOC less than 120v
2x SRNE 5k - 2x 120v SRNE 5k wired in split phase. Simple to install for a first timer. Cheaper and much lighter and smaller. 2 points of failure, but can still run 1 120v leg until component swapped.
SRNE 10k (or 6000XP) - Even more simple. Single point of failure (any failure would take the RV out). Perhaps a bit too big for the passthrough. About the same price as 2x 5ks. 8k vs 10k, basically same weight and form factor so why not get more power? *I have seen many use EG4's 6000xp with varied success, however if I can get more power for similar size and cost...)
Concerns
These are my biggest concerns that I'm having difficult time addressing.
Ground Bonding
I believe with the Quattro's, this is automatically done. From what I've read, this setting would need to be manually changed on the SRNE inverters.
How difficult is it to change on SRNE? We plan to primarily not use grid. If it only takes an additional 2 minutes as part of the camp setup when we park somewhere that has hookups, I'm not too worried about that.
Auto Gen Start
One must have feature is that once batteries get to X%, the generator would auto start to recharge the batteries and shutoff at specified logic.
Would also be nice to run generator for extra power if power consumption >Xw (like 3-7pm in the summer to power A/C's instead of just using PV/battery).
I have seen this done using the Cerbo and a timer relay control. (My Gen has a prime/stop and start, so not 2 wire. The timed relay can be programmed to prime for X, then start.)
I have no idea if this is possible with the SRNE and couldn't find much in the manual on the subject. I see the dry contact for Gen Start, but unsure about the programmability and if it would work with the timed relay controller like the Cerbo.
Autoformer Required
If I'm not mistaken, because my generator (Onan 5500) outputs 120v single phase, I will need to use and autoformer to run split phase into the inverters for charging bypass.
Alternatively I could wire a chargeverter to the generator, but is this as efficient?
Could I do 1 leg into the inverter and 1 into the chargeverter? Is this even worth it and would it require changing inverter settings every time I wanted to do this?
Idle Draw
From what I've read, Victron hands down wins idle draw..
*I don't know how exactly this works, but there will almost always be AC draw on the inverters. Refrigerator, TV's, Computers & networking equip,.
Is this idle draw less relevant when there is always a load?
That being said, Victron components take up significantly more space, weigh more, and cost significantly more.
For the cost and weight, I could add another 5kw of power which should offset any power loss and likely have a net gain.
Visual Assistant
I love to tinker and collect and view data. I will certainly be running Solar assistant or CerboGX.
As far as I know, I cannot issue remote commands to the inverter via Solar Assistant, only via Victron CerboGX to Victron inverter.
Is this correct? Is this ability really even that useful?
QTY Weight lbs (total) Cost USD
Option 1
Quattro 5kva 2 132 $3,359.14
MPPT Victron (TBD) 2 5 $700.00
Autoformer 100a 1 30 $510.00
Cerbo GX (kit) 1 $575.00
$5,144.14
Option 2
5k SRNE (SGP) 2 52 $1,518.00
MPPT 4 0 $0.00
Autoformer 100a 1 30 $510.00
Solar-Assistant 1 2 $210.00
$2,238.00
Option 3
10k SRNE (SGP) 1 54 $1,690.00
MPPT 2 0 $0.00
Autoformer 100a 1 30 $510.00
Solar-Assistant 1 2 $210.00
$2,410.00
Here it all is! Victron is over 2x the cost and 2x the weight.
I feel like I've been chasing the rabbit around the hole and I'm no closer to catching it. I really need to pull the trigger and get the components on order.
I would love any input or advice the community may be able to share.
Thanks again.
I am building out a power system for our 46' 5th wheel as we begin our fulltime RV living.
We plan on being nomad's for several years staying mostly in boondocking sites. We work remotely and have dogs so we need to be able to run A/C's (if needed) and power our workstations, monitors, network, etc.
We have 3 standard RV dometic penguin II A/Cs (2 with heatpump). I know that I can't plan to run all 3 all day, but would like the system sized large enough that I could run all 3 plus the microwave, tv, fridge, computer if I wanted (even for just 1 hour). I can run the generator if I need to run them a lot. Ideally we would not be parked in a heat dome, but.. that might be hard to do sometimes.
This has led me down the ~10kva/10kw 48v inverter path. *I have not performed a power audit yet as we are still living / working in our house, it's currently 100+ degrees and we have no grid connection at the RV's location (family members land).
I would like to have 25-30kwh of power stored via ecoworthy server rack batteries in the storage passthrough. We are towing with a converted Semi Tractor "toterhome" so pinweight isn't a big issue. I will put as many solar panels on the roof as I can fit. I have not determined what panels due to required VOC for MPPT. Currently have 2 sets of wires running from roof to passthrough. Potentially adding an additional ground array (after real world testing) if needed.
As the weather starts cooling down I plan to begin installing the system so that I can move into the RV and work on completing the install (inevitably troubleshooting it) and breaking it in.
Since we're currently stationary, I can lay the panels on the ground for now to obtain power as well as running the generator when additional power/charging is needed. Then work on roof mount (unistrut) as time and weather permit.
At this point I've spent 100+ hours researching components and other builds. I've spoken with a couple professional RV solar installers (one who said 12v only for RVs, one said 48v only for this size). I'm not at all concerned about having 12v 48v and 120v systems in my RV. I'm not an electrician but work in the technology industry and have had many hobbies that use various battery types and voltages.
I've been looking at using Ecoworthy and SRNE components due to their cost, reputation, and receiving a random guy on the internet named Will's blessing. *Thanks for everything you do Will!*
I am now asking for your thoughts on the potential systems that I am considering and if anyone has any experience with the non-Victron components. Am I totally missing something?
Thanks for taking the time to read this and for providing any input.
46 ft 5th wheel
50amp 120v (no 240v appliances)
Onan 5500 Genset Single Phase 2x 30a breaker
System comparison
Batteries - Looking at 5-6x Ecoworthy V3 Server Rack 48v 100ah to be able to utilize comms.
2x Victron Quattro 5k - I know this has been done in many RV's and hits all my requirements. However, it's expensive, heavy, and large. Much more complex. Can still run 1 leg if an inverter fails. PV Charging/Inverter can fail separately. Min VOC less than 120v
2x SRNE 5k - 2x 120v SRNE 5k wired in split phase. Simple to install for a first timer. Cheaper and much lighter and smaller. 2 points of failure, but can still run 1 120v leg until component swapped.
SRNE 10k (or 6000XP) - Even more simple. Single point of failure (any failure would take the RV out). Perhaps a bit too big for the passthrough. About the same price as 2x 5ks. 8k vs 10k, basically same weight and form factor so why not get more power? *I have seen many use EG4's 6000xp with varied success, however if I can get more power for similar size and cost...)
Concerns
These are my biggest concerns that I'm having difficult time addressing.
Ground Bonding
I believe with the Quattro's, this is automatically done. From what I've read, this setting would need to be manually changed on the SRNE inverters.
How difficult is it to change on SRNE? We plan to primarily not use grid. If it only takes an additional 2 minutes as part of the camp setup when we park somewhere that has hookups, I'm not too worried about that.
Auto Gen Start
One must have feature is that once batteries get to X%, the generator would auto start to recharge the batteries and shutoff at specified logic.
Would also be nice to run generator for extra power if power consumption >Xw (like 3-7pm in the summer to power A/C's instead of just using PV/battery).
I have seen this done using the Cerbo and a timer relay control. (My Gen has a prime/stop and start, so not 2 wire. The timed relay can be programmed to prime for X, then start.)
I have no idea if this is possible with the SRNE and couldn't find much in the manual on the subject. I see the dry contact for Gen Start, but unsure about the programmability and if it would work with the timed relay controller like the Cerbo.
Autoformer Required
If I'm not mistaken, because my generator (Onan 5500) outputs 120v single phase, I will need to use and autoformer to run split phase into the inverters for charging bypass.
Alternatively I could wire a chargeverter to the generator, but is this as efficient?
Could I do 1 leg into the inverter and 1 into the chargeverter? Is this even worth it and would it require changing inverter settings every time I wanted to do this?
Idle Draw
From what I've read, Victron hands down wins idle draw..
*I don't know how exactly this works, but there will almost always be AC draw on the inverters. Refrigerator, TV's, Computers & networking equip,.
Is this idle draw less relevant when there is always a load?
That being said, Victron components take up significantly more space, weigh more, and cost significantly more.
For the cost and weight, I could add another 5kw of power which should offset any power loss and likely have a net gain.
Visual Assistant
I love to tinker and collect and view data. I will certainly be running Solar assistant or CerboGX.
As far as I know, I cannot issue remote commands to the inverter via Solar Assistant, only via Victron CerboGX to Victron inverter.
Is this correct? Is this ability really even that useful?
QTY Weight lbs (total) Cost USD
Option 1
Quattro 5kva 2 132 $3,359.14
MPPT Victron (TBD) 2 5 $700.00
Autoformer 100a 1 30 $510.00
Cerbo GX (kit) 1 $575.00
$5,144.14
Option 2
5k SRNE (SGP) 2 52 $1,518.00
MPPT 4 0 $0.00
Autoformer 100a 1 30 $510.00
Solar-Assistant 1 2 $210.00
$2,238.00
Option 3
10k SRNE (SGP) 1 54 $1,690.00
MPPT 2 0 $0.00
Autoformer 100a 1 30 $510.00
Solar-Assistant 1 2 $210.00
$2,410.00
Here it all is! Victron is over 2x the cost and 2x the weight.
I feel like I've been chasing the rabbit around the hole and I'm no closer to catching it. I really need to pull the trigger and get the components on order.
I would love any input or advice the community may be able to share.
Thanks again.