The fuse size will be determined by your load current.... not battery size.
1) Since you have a 16S BMS I am assuming a 48V system.
2) For example purposes, I will assume you have a 3000W inverter that is 90% efficient.
3) That means the the battery will have to supply 3000W/.9=3333W when the inverter is maxed out.
4) That means the current at max continuous load if the battery is almost empty will be 3333W/48V=69.4A.
5) You never want to run a fuse at it's full capacity so you need to add 25% so the fuse size should be at least 69.4*1.25=86.8.
Note: A class T fuse is very fast acting. That means surge currents from inductive loads have the possibility of blowing the fuse. Therefor
25% is the *minimum* headroom I would advise.
6) I have not shopped for a 90A class T, but it might not be available so you will probably use a 100A class T.
7)
*Any* wire down-stream of the Fuse that does not have an additional fuse on it must be large enough to handle the trip current of the fuse. (For 100A, that is a 4 AWG wire
I would advise a review of this paper:
To get the paper, click on the orange button at the top of the page The attached presentation gives the fundamentals for picking fuse/breaker sizes and describes where in the circuit they should be placed. You can download the presentation by...
diysolarforum.com
NO. If your inverter or some other device can provide the data you want in the way you want it, an additional shunt is not necessary. In some cases, adding a shunt is necessary to get the the data you want in the way you want it. Since we don't know the other components of the system, we don't know if SOC is available over LAN from them.
Only the obvious: Preparing whatever case you will use, preparing whatever compression (if any) you will use, Acquiring all the incidentals like wire, lugs, fuses and tools you will need. etc
I used to ALWAYS do a capacity test on individual cells. However, after a while I realized the results did not change what I did next...which was to assemble the battery. Consequently I never do per-cell capacity tests any more... the extra data is not worth the extra effort to me (Many people have the opposite opinion on this...it is up to your personal value set). Heck, I have built whole batteries without even doing a battery capacity test before I put them into service. Granted, the data of capacity testing is interesting....but it rarely changes what I end up doing.