Well nobody trashed the Victron dealer who told me the AutoTransformer (placed in Location A) would solve the problem of powering the GSHP and providing 120V to the cabin. So it seems that this should work.
Thank you fellas for digging into that.
@Hedges do you agree the most that GSHP will demand is 4600W which is no issue for the Multiplus supplying 8KW?
I sure appreciate you guys keeping me out of trouble by providing your generous expertise and making this forum a goldmine for dummmies like me.
Total unit FLA 25.3A x 230V = 5819 VA
So you at least need that.
"Fan motor FLA 3.9A", let's assume 19.5A starting surge, 15.6 A more than running. 3588W more.
If you're lucky, fan is started up first while compressor isn't running.
But at least plan on 9.4kW surge. I think you should have a bit of extra power available, and obviously I can't guarantee we've interpreted the data sheet correctly and conservatively.
I find no mention of "PF" or "Power Factor".
I would like inverter drives to present a simulated resistive load (PF = 1.0, current drawn is a perfect sine wave), but some just swallow little gulps of current off the peak of voltage sine wave.
Such loads could present a larger demand on your inverter.
Maybe ask vendor of GSHP about what size generator and inverter are needed to run it.