sunshine_eggo
Happy Breffast!
Doesn't appear so....
No. He's smarter than I am. I missed the Fan motor.
Doesn't appear so....
No. He's smarter than I am. I missed the Fan motor.
If you are doing split phase over the long runs what purpose do the auto transformers serve?No. You'll need to run 4 wires now. L1, L2, N and G. It probably comes down to the following:
Is it cheaper to run 4 wires to each cabin, or is it cheaper to run 2 wires to each cabin and have an autotransformer at each cabin? I would ask your dealer about that.
Doesn't appear so....
I just like to be a contrarian. So I kept digging.
My professors hated me. A 'prime' government contractor, too. I basically told them their baby was ugly.
(but I guess they got the last laugh, when we paid them $millions to do it over.)
Perfect. So the expensive wire just tripled because whatever could flow through one wire before has been split up and needs to go through three big wires now? I knew I didn't like science. The hits just keep on coming!
B and C are very far from each other with A between them. 800 feet or so.
One question I still have on the Victron stuff. The two SmartSolar charge controllers 450/200 can deliver 400 amps for charging. But the Multiplus 2 48/8000 says its max battery charging is 110 amps.
What is charging the batteries and if it is the Multiplus is it going to be limited to 110 amps?
I ask as my Friday night is getting less fun...
You're the kind of guy many don't like. But need. And they don't like that they need you.
But I like you AND need you!
Do does that mean the 450/200 SmartSolar charge controllers will provide 200 amps (each) to charge the battery and the MultiPlus might provide an additional 110amps?I think Multiplus takes in power from its AC input (e.g. generator) and dumps 110A into battery.
You're free to connect SmartSolar, a DC generator, or any other source to battery as well.
Probably Multiplus wants to know how many amps. Or, with lithium and BMS, maybe it just asks.
Part of the Victron ecosystem is a battery shunt, which would measure net current into the battery considering various charging sources, inverters, DC loads. That would be needed if lead-acid, maybe not necessary for lithium with communication to BMS.
Do does that mean the 450/200 SmartSolar charge controllers will provide 200 amps (each) to charge the battery and the MultiPlus might provide an additional 110amps?
Please say yes....
If you are doing split phase over the long runs what purpose do the auto transformers serve?
Well, the good news *I think* is that the Multi-Plus II 48/8000 model has a peak power of 15,000W so I'm assuming that will take care of the surge.
If not I'm going to switch to coal.
One question I still have on the Victron stuff. The two SmartSolar charge controllers 450/200 can deliver 400 amps for charging. But the Multiplus 2 48/8000 says its max battery charging is 110 amps.
What is charging the batteries and if it is the Multiplus is it going to be limited to 110 amps?
I ask as my Friday night is getting less fun...
I think Multiplus takes in power from its AC input (e.g. generator) and dumps 110A into battery.
You're free to connect SmartSolar, a DC generator, or any other source to battery as well.
Probably Multiplus wants to know how many amps. Or, with lithium and BMS, maybe it just asks.
Part of the Victron ecosystem is a battery shunt, which would measure net current into the battery considering various charging sources, inverters, DC loads. That would be needed if lead-acid, maybe not necessary for lithium with communication to BMS.
Thank you. That makes sense.Yes.
Each SCC can provide 200A. If MultiPlus has AC feeding it and it's charger function is rated 110A, that goes in too. There is going to be some AC amperage limit on the input, so if all 6kW or so is going to battery charging that may limit how much can feed through. You said Honda 7000, so I guess there's only 1kW left anyway.
Figure out what you're doing to keep batteries warm. The charge the can accept will be reduced when cold. BMS probably implements a low-temperature charge disconnect. I don't know which if any of your equipment would reduce charge current if BMS asks them to. I also don't know if BMS is aware of reduced current limits at low temperatures.
Possibly the only controls you will have is max current setting of SCC and disconnect temperature of BMS. In which case I would suggest selecting a max current, a temperature cutoff where that current is acceptable, and try to keep batteries heated above that temperature.
So far we do not see the wiring diagram yet, I think OP should provide it so we can inspect and give suggestions and see if there is something amiss or not.Don't take this the wong way, but is this seriously a DIY job? I would highly recommend getting a solar Installer for something of this size and scale.
I doubt it. Not for me anyway.Don't take this the wong way, but is this seriously a DIY job? I would highly recommend getting a solar Installer for something of this size and scale.
I agree. Hopefully I'll be able to get that done before long.So far we do not see the wiring diagram yet, I think OP should provide it so we can inspect and give suggestions and see if there is something amiss or not.